jar546
CBO
although I wouldn’t fail this inspection for just this. It is our policy that when you call for a rough inspection, a rough wiring inspection, that all of your grounds and neutrals and pigtails are in place so the only thing left for you to do is attach your devices, not start on twisting and adding wires. So the photo below shows something that if the electrician was present, I would have him take care of real quickly, but in this case, the electrician was not present, and there were other issues therefore, the inspection failed for not being ready. Don’t forget that the next time we are out there as electrical inspectors, it will be when all of the devices have been installed so we will never be able to knowif the proper grounds and neutrals were put together. This is also important because there are times when they bring two different circuits into a switch box and they will tie all of the neutrals together, even though they are from separate circuits, which is a violation.