• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

When to upgrade visual notification appliances

Brian 2

Registered User
Joined
May 18, 2017
Messages
17
Location
Denver
Under the 2015 IFC/IEBC. Level 2 alteration in an existing building with an existing horn only fire alarm system. Tenant space is gutted and rebuilt. Is there any Code basis requiring an upgrade to visual notification in the tenant space? IEBC appears silent until you get to Level 3 alterations.
 
You can't make the building any less safe than it was prior to the alteration. Thus, the horn-only device must be reused or replaced with at least a similarly functioning device.
 
I thinking they should already be there.

If not than we require them to be installed,

Have not been questioned on it yet

Per IFC, and so the system meets NFPA 72 for dba level

Plus seems like it would be an ADA requirement for them to be installed??
 
Plus seems like it would be an ADA requirement for them to be installed??
Per the 2010 ADA Standards:
215.1 General. Where fire alarm systems provide audible alarm coverage, alarms shall comply with 215.
EXCEPTION: In existing facilities, visible alarms shall not be required except where an existing fire alarm system is upgraded or replaced, or a new fire alarm system is installed.​
 
  • Like
Reactions: cda
ADA would only come in with the apartment designed for that. a normal apartment would not need a horn and strobe in them.
 