• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Where to plug in an office projector mounted on the suspended ceiling

jar546

Forum Coordinator
Joined
Oct 16, 2009
Messages
11,076
Location
Somewhere Too Hot & Humid
Many conference rooms in office buildings and other commercial establishments have projectors mounted on suspended ceilings, often with a lot of data cable hooked up too. Is it acceptable to have the receptacle that serves the projector permanently mounted inside/above the ceiling?

So, is the receptacle the issue or does it become an issue when they plug in the projector?

What code sections cover this installation?
 
Is it acceptable to have the receptacle that serves the projector permanently mounted inside/above the ceiling? So, is the receptacle the issue or does it become an issue when they plug in the projector? What code sections cover this installation?

A receptacle is permitted above the drop ceiling, Its the cord that's not permitted, NEC 400.8 (2) and (5). Same thing when the bar owner wants to punch a hole in the CT for his Bud light window sign.
 
400.8 Uses Not Permitted. Unless specifically permitted in 400.7, flexible cords and cables shall not be used for the following:

(2) Where run through holes in walls, structural ceilings, suspended ceilings, dropped ceilings, or floors

(5) Where concealed by walls, floors, or ceilings or located above suspended or dropped ceilings
 
It is a bit of a stretch to label a projector as a luminaire. However, 400.7 includes luminaires and 400.8 removes it's restrictions simply because 400.7 includes luminaires. I think that we would be better served if 400.8 enumerated the restrictions that are waived. For example, "above or through a suspended ceiling" seems like no big deal....."Where concealed by walls, floors, or ceilings" is taking it too far. How about "Where run through holes in walls"?
 
It is a bit of a stretch to label a projector as a luminaire. However, 400.7 includes luminaires and 400.8 removes it's restrictions simply because 400.7 includes luminaires. I think that we would be better served if 400.8 enumerated the restrictions that are waived. For example, "above or through a suspended ceiling" seems like no big deal....."Where concealed by walls, floors, or ceilings" is taking it too far. How about "Where run through holes in walls"?

yeah, no one is saying that a projector is a luminaire. You were asking about how 400.7 would not change the result but it could for luminaires. That's all.
 