The following is my research on some questions presented to me at work today.
Code Research
Question;
Is there a minimum number of risers where you do not need a handrail?
Can you have one handrail?
Can you have open risers?
ADA 2010 Standards: Titles II and III & ICC/ANSI A117.1-2003
504 Stairways
504.3 Open Risers. Open risers are not permitted.
504.6 Handrails. Stairs shall have handrails complying with 505.
505 Handrails
505.2 Where Required. Handrails shall be provided on both sides of stairs and ramps.
2006 INTERNATIONAL BUILDING CODE®
1009.10 Handrails. Stairways shall have handrails on each side and shall comply with Section 1012.
3. Decks, patios and walkways that have a single change in elevation where the landing depth on each side of the change of elevation is greater than what is required for a landing do not require handrails.
COMMENT:
Open Risers; The IBC Section 1009.3.3 does allow open risers in Exception #1. However, the opening cannot permit the passage of a 4” sphere. The Accessibility Codes do not allow open risers in any condition for a stair used as an accessible route.
Handrails; The IBC Section 1009.10 has an exception to not require handrails; however, the Accessibility Codes do require handrails. The IBC also allows one handrail for certain occupancies but the Accessibility Codes requires handrails on each side of the stair or ramp and does not mention occupancy use except it does mention Assembly.
So the question is now, if the IBC does not require a handrail, as 1009.10 Exception #3 states, does the Accessibility Codes require the handrail even for one riser? The IBC Exception referenced would allow one riser. Feel free to respond the the other questions in the body of the research.
Code Research
Question;
504 Stairways
505 Handrails
COMMENT: