• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Why You Should Look Inside P-Taps

jar546

Forum Coordinator
Joined
Oct 16, 2009
Messages
11,078
Location
Somewhere Too Hot & Humid
Whenever you see big wire and small wire in the same P-Tap, you need to look a little closer. P-Taps have a minimum and maximum wire size they are rated for. In this case I noticed 600MCM and 3/0 at the P-Tap along with a #6. The Tap was rated #4 to 600MCM and as a result, you can see what the electrician did to make it work. NEC 110.3(B)
IMG_5361.JPG
 