Won Door

cda

SAWHORSE
Joined
Oct 19, 2009
Messages
20,962
Location
Basement
So have not done a new Won door in forever. Use to like them.

So say the occupant load going through the Won Door is 800.

What is the answer to item 8 below???

"""minimum required width"""


1010.1.4.3 Special Purpose Horizontal Sliding, Accordion or Folding Doors

In other than Group H occupancies, special purpose horizontal sliding, accordion or folding door assemblies permitted to be a component of a means of egress in accordance with Exception 6 to Section 1010.1.2 shall comply with all of the following criteria:
  1. The doors shall be power operated and shall be capable of being operated manually in the event of power failure.
  2. The doors shall be openable by a simple method from both sides without special knowledge or effort.
  3. The force required to operate the door shall not exceed 30 pounds (133 N) to set the door in motion and 15 pounds (67 N) to close the door or open it to the minimum required width.
  4. The door shall be openable with a force not to exceed 15 pounds (67 N) when a force of 250 pounds (1100 N) is applied perpendicular to the door adjacent to the operating device.
  5. The door assembly shall comply with the applicable fire protection rating and, where rated, shall be self-closing or automatic closing by smoke detection in accordance with Section 716.5.9.3, shall be installed in accordance with NFPA 80 and shall comply with Section 716.
  6. The door assembly shall have an integrated standby power supply.
  7. The door assembly power supply shall be electrically supervised.
  8. The door shall open to the minimum required width within 10 seconds after activation of the operating device.
 
IBC 2018 1005.3.2. Calculation is occupant load times a factor of 0.2 inch. That is not for stairway, just "other egress components." It has 3 exceptions so read those to see if they apply to your situation.

Hope this helps.
 
  • Like
Reactions: cda
Nicely done JRice....first post and you are spot on. What industry are you joining us from? I'd say welcome, but looks like you have been a member for almost 10-years now.


1005.3.2 Other Egress Components
The capacity, in inches, of means of egress components other than stairways shall be calculated by multiplying the occupant load served by such component by a means of egress capacity factor of 0.2 inch (5.1 mm) per occupant.

Exceptions:

  1. For other than Group H and I-2 occupancies, the capacity, in inches, of means of egress components other than stairways shall be calculated by multiplying the occupant load served by such component by a means of egress capacity factor of 0.15 inch (3.8 mm) per occupant in buildings equipped throughout with an automatic sprinkler system installed in accordance with Section 903.3.1.1 or 903.3.1.2 and an emergency voice/ alarm communication system in accordance with Section 907.5.2.2.
  2. Facilities with smoke-protected assembly seating shall be permitted to use the capacity factors in Table 1029.6.2 indicated for level or ramped aisles for means of egress components other than stairways where the entire path for means of egress from the seating to the exit discharge is provided with a smoke control system complying with Section 909.
  3. Facilities with outdoor smoke-protected assembly seating shall be permitted to the capacity factors in Section 1029.6.3 indicated for level or ramped aisles for means of egress components other than stairways where the entire path for means of egress from the seating to the exit discharge is open to the outdoors.
 
So if my Kindergarten math is correct

160 inches?

13 feet?????


""The door shall open to the minimum required width within 10 seconds after activation of the operating device."""
 
Ok maybe I should have read,,,

What the code said book first:::


DD97DCD9-09E7-4B42-9AA5-888AB77A341C.jpeg



Not sure if 1005.3.2 and required width are the same, or always the same??
 