1. Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by clicking here: Upgrades
    Dismiss Notice

Wood foundation wall

Discussion in 'Residential Foundation Codes' started by retire09, Nov 2, 2011.

  1. retire09

    retire09 Silver Member

    Joined:
    Feb 19, 2010
    Messages:
    365
    Likes Received:
    1
    I have an existing residence with a wood foundation wall constructed with a treated sole plate and untreated 2x6 studs with a galvanized metal material on the outside. R404.2 requires wood foundation walls to be constructed in accordance with R403.1(3).

    Figure R403.1(3) would require treated studs with treated plywood on the outside.

    Could a wood preservative be applied to the bottoms of the studs in contact with the sole plate or some means provided to prevent moisture from being drawn into the studs?

    The existing is not in accordance with code but can it still meet the intent of the code by alternative methods?

    Any suggestions?
     
  2. steveray

    steveray Sawhorse

    Joined:
    Nov 25, 2009
    Messages:
    6,702
    Likes Received:
    936
    Its existing.....why are you trying to make it right now?
     
  3. Mark K

    Mark K Platinum Member

    Joined:
    May 12, 2010
    Messages:
    1,525
    Likes Received:
    139
    Brushing on some treatment does not provide the necessary penetration into the wood.

    The preservative is not intended to prevent moisture from being drawn into the stud but rather to prevent the growth of organisms that rot the wood. There are other mechanisms that allow moisture to get into the wood.
     
  4. gbhammer

    gbhammer Platinum Member

    Joined:
    Aug 1, 2011
    Messages:
    1,279
    Likes Received:
    5
    How long has it been there? If it is not rotted yet then what type of wood is it. It may be decay-resistant heartwood of redwood, black locust, or cedars.
     
  5. retire09

    retire09 Silver Member

    Joined:
    Feb 19, 2010
    Messages:
    365
    Likes Received:
    1
    The house is 4-5 years old. the studs are standard #2 Fir. Here in Alaska this would probably last forever.

    The problem was discovered by a realestate home inspector.

    The buyers are wanting the sellers to correct the problem.

    The estimated cost is $20,000.

    I'm not so sure from a code or a practical standpoint that this is all that bad.

    This was approved by the previous building inspector.

    Just looking for other opinions.
     
  6. steveray

    steveray Sawhorse

    Joined:
    Nov 25, 2009
    Messages:
    6,702
    Likes Received:
    936
    I wouldn't want to sign off on it as a BO......maybe a letter from a DP would make them all warm and fuzzy?
     
  7. codeworks

    codeworks Gold Member

    Joined:
    Jun 12, 2011
    Messages:
    580
    Likes Received:
    3
    how does the real estate inspector get you reinvolved at this point? it was approved when it was built. it's existing/noncomplying ? . did it comply when (i've been out of this a while thats why i'm asking the question) it was built, or was it constructed under "approved alternative methods" .
     
  8. Mark K

    Mark K Platinum Member

    Joined:
    May 12, 2010
    Messages:
    1,525
    Likes Received:
    139
    If there is no record that this deviation was approved by the building official/inspector then it could be argued to be a violation of the code.
     
  9. ICE

    ICE Sawhorse

    Joined:
    Jun 23, 2011
    Messages:
    8,477
    Likes Received:
    927
    Whether it was approved or not is not the deciding factor. It's either a violation or it's not.
     
  10. JBI

    JBI Sawhorse

    Joined:
    Oct 17, 2009
    Messages:
    2,788
    Likes Received:
    288
    Don't all wood framed floors for the first floor of all wood framed homes sit on PT plates?

    The question is indeed whether or not it met code (and complied with the approved plans) at time of construction.

    Next question could be "Is this an approveable alternative method in light of the galvanized metal exterior?"

    Immediately followed by "Can they find an Engineer that will provide a sound engineering methodology to justify the alternative?"

    Nice catch by the Home Inspector for what it's worth.
     
  11. DRP

    DRP Gold Member

    Joined:
    Sep 14, 2010
    Messages:
    529
    Likes Received:
    0
    If it is exposed, which I assume since it was seen, the wood could be saturated with boracare or a similar glycol borate solution which diffuses in deeply if applied well. That would prevent decay fungi from growing as long as there is no sink to leach the borate out, which there doesn't sound like there is. Non code but it would do the job. Lots of qualifications, I doubt it would make the sale happen. Would sistering treated studs alongside existing allow you to approve it?
     
  12. Mark K

    Mark K Platinum Member

    Joined:
    May 12, 2010
    Messages:
    1,525
    Likes Received:
    139
    ICE

    If, although unlikely, the building official was aware of the violation and approved it in accordance with IBC 104.11 (similar language in IRC) then it is no longer a code violation. This would require that somebody had a record that it was approved as an alternate means of compliance. On the other hand if all that exists is the approval of the building permit then it is a violation allowing the building official to take action to mitigate the violation.
     