• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Wood Frame Nailing of Ceiling Joist Overlap

jar546

Forum Coordinator
Joined
Oct 16, 2009
Messages
11,064
Location
Somewhere Too Hot & Humid
Ranch house 30psf ground snow load. House is 28' wide with a 5/12 pitched roof and the builder will has specified 2x8 ceiling joists 16" O.C. with a minimum of a 3" overlap due to rafter thrust conditions being present. What size and how many nails should there be at the ceiling joist overlap?
 
jar546 said:
Nope, hence the reason I posted this. Another common overlooked section of the IRC. Try again
In that case....we can't answer because we don't have the OC framing spacing, and wether or not the nails are clinched.....

We have a pretty decent history of good framers up here, and this has not been an issue......but it is getting worse by the year....

And we won't even get into when a flush beam is involved....
 
7 16d commons in the last 3" of a 2x8 seems like a bad idea.....but we never lapped by just 3"

Jeff....have they revised this yet? 2003 IRC Pretty serious conflict from 3 10s to 7 16s....

R802.3.2 Ceiling joists lapped.

Ends of ceiling joists shall be lapped a minimum of 3 inches (76 mm) or butted over bearing partitions or beams and toenailed to the bearing member. When ceiling joists are used to provide resistance to rafter thrust, lapped joists shall be nailed together in accordance with Table R602.3(1) and butted joists shall be tied together in a manner to resist such thrust.
 
Minimum 3" overlap as required by code. Minimum does not mean they can't do more.

The moral of the story is that the requirement for nailing this overlap in accordance with 802.5.1(9) per the 2009 IRC is often overlooked by both inspectors and framers. Each time we fail someone for non-compliance we always hear how they just built the same house in another town and they made sure they had the 3-10d nails only.

I am hoping that this will enlighten anyone who comes to this forum and makes it a more educational experience and helps the cause.
 