• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

would you allow this?

ICE

Oh Well
Joined
Jun 23, 2011
Messages
12,919
Location
California
The service panel will be removed and a new service has been installed on the other side of the house. Rather than create a J-box out of the existing service enclosure, a 1R panel enclosure has been installed behind the access panel as shown. The contractor tells me that he has done this many times and never gotten any resistance from an inspector. He feels that the access cover provides a 3R rating and therefor the 1R enclosure is legitimate. He also stated that there is no 3R sub-panel available in the marketplace but I found several.

This is part of a $100K addition/remodel on a 2 million dollar house. Now that should not influence a decision but his crying about the cost falls on deaf ears.



 
Last edited:
# ~ # ~ #

Article 110.20 in the `08 NEC requires the electrical enclosure
to be marked with an Enclosure Type number and be
suitable for the location.........The 1R cover does not meet the
requirement to be rainproof like a 3R does.

The whole enclosure must be rated 3R.


# ~ # ~ #
 