• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Yard box (gas shut off valve) identification?

insp steve

Member
Joined
Jan 23, 2012
Messages
7
Location
Riverside, California
I am stuck on this one... the contractor installed a cast Iron lid (8" dia) on the, gas shut off valve, yard box. He ground off the existing label (cast raised label). I need help locating the code section that requires labeling.

NOTE: this is not the main (metered) valve at the street. This is a new valve tapped into an existing medium pressure natural gas 3" line, connecting the new science wing on an existing campus, that is buried 2' below the surface. There is also and SOV at the building exterior, where it enters above ground.

PS, I will also post this in the other forum.

thanks,

steve.
 
409.3.3 Identification of shutoff valves. Each house line shutoff valve shall be plainly marked with an identification tag attached by the installer so that the piping systems supplied by such valves are readily identified.

409.4 MPRegulator valves. A listed shutoff valve shall be installed immediately ahead of each MP regulator.

Hate to say it, but I don't think the code section exists..... Do I think it is a good idea, absolutely.

Is it required by the code - Don't think so

However, What was the new wing designed as, an addition or with fire walls...
 