Someone check my math. Are you aware of this?
To illustrate a situation where a wire could fit into a 1.5-inch Schedule 40 PVC conduit but not into a 1.5-inch Schedule 80 PVC conduit, according to the NEC, let's consider a 4 AWG THHN/THWN copper wire.
The approximate area of a 4 AWG copper THHN/THWN wire is about 0.1293 square inches per conductor. According to the NEC, the conduit fill should generally not exceed 40% for more than two conductors.
The approximate internal area for 1.5-inch Schedule 40 PVC conduit is 1.767 square inches, while for 1.5-inch Schedule 80 PVC conduit, it's 1.443 square inches.
To illustrate a situation where a wire could fit into a 1.5-inch Schedule 40 PVC conduit but not into a 1.5-inch Schedule 80 PVC conduit, according to the NEC, let's consider a 4 AWG THHN/THWN copper wire.
The approximate area of a 4 AWG copper THHN/THWN wire is about 0.1293 square inches per conductor. According to the NEC, the conduit fill should generally not exceed 40% for more than two conductors.
The approximate internal area for 1.5-inch Schedule 40 PVC conduit is 1.767 square inches, while for 1.5-inch Schedule 80 PVC conduit, it's 1.443 square inches.
Schedule 40 PVC Conduit:
- Maximum fill would be 1.767×0.4=0.70681.767×0.4=0.7068 square inches.
- Number of conductors that can fit: 0.7068÷0.1293≈5.460.7068÷0.1293≈5.46.
- Rounding down, 5 conductors of 4 AWG could fit into a 1.5-inch Schedule 40 PVC conduit.
Schedule 80 PVC Conduit:
- Maximum fill would be 1.443×0.4=0.57721.443×0.4=0.5772 square inches.
- Number of conductors that can fit: 0.5772÷0.1293≈4.460.5772÷0.1293≈4.46.
- Rounding down, only 4 conductors of 4 AWG could fit into a 1.5-inch Schedule 80 PVC conduit.