• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Zone Air Distribution Effectiveness

Mech

Registered User
Joined
Oct 30, 2009
Messages
1,037
Location
Eastern PA
2009 IMC

Automotive Repair Garage

403.3.1 Zone Outdoor Airflow

403.3.1.1 - 403.3.1.3

When providing ventilation based solely on exhaust airflow, does the Zone Air Distribution Effectiveness factor get used? The equation for zone outdoor airflow is Voz = Vbz / Ez. It does not directly include the exhaust airflow rate column in Table 403.3. Or do I calculate the total exhaust airflow required base on area size and use that as the value Vbz?

Thanks in advance.
 
Per IMC 403.1.1:

Vbz=RpPz+RaAz

Per IMC Table 403, for Repair Garage, Rp = 0, Ra = 0

Therefore and thus, Vbz = 0 and Voz = 0

Outside air is not required in a repair garage, exhaust is. You do need to provide make-up air of course, and one way of doing that is with outside air, but that is the designer's choice.
 