acheiving fire rating in wood stud/gypsum board drop ceiling
sal
medford
This is for a 1 hour stc 50 requirement in a ceiling floor assembly. I have an existing building and a wood stud drop ceiling. Was going to specify 2 layers of type "x" over rc-1 Chanel at the drop ceiling, then roxul between the 2x6 studs at the floor structure above. Is this a good solution?
I can't find a similar ul for this type of assembly but figure 40+40 min for 2 layers of type x will cover me for over an hour. I think just 1 layer would have sufficed bu read in the gypsum association manual that if you said insulation to add another layer of type X.
if you need a true rating, look to the gyp board manufactures for a complete assembly meathod. UL among others lists spicific construction to achive the desired rating. you can not just add another layer to somthing.
i cannot find anything for a similar drop ceiling in the manual. Should a 'true" ceiling be installed in the upper ceiling in this case? The drop ceiling below just cosmetic?
That would be best/ easiest...otherwise you have to rate all of the penetrations of the "dropped" ceiling (light fixtures, HVAC registers, etc...)
atleast 50-60 years, its all balloon framed.
I would have liked to instal 2 layers of gyp at the drop ceiling,, but don't know if that created plenum space causes heat build-up.
If instaling rated 'real" ceiling above, would the drop ceiling below be an issue for heat build-up?
New construction requires a true 1 hour rating, but this is an existing building. Does this make it the inspector's call?
When using the calculated method, the code states type "x" gyp is 40 min. So why wouldn't 2 layers that suffice ( if we are not going for a tested assembly)
Does the calculated method specify for method of assembly? Where is this in the code?
Gypsum Association Fire Resistance Design Manual construction FC-5406 sounds similar to what you're describing. The 2 layers of 5/8" type X provide 1-hour protection for the framing.
Firestopping at the dropped ceiling will be critical, as well as protection of penetrations..
Roxul appears to be an interesting product not often seen south of you. I could not find any standard details on their website.
It is noncombustable and therefor fire resistant but can it be added to flammable material to protect it? If so, how much is required to do so?
2012 IBC Table 722.2.1.4(2) that gives the calculated fire resistance ratings for GWB is for the fire exposed side of walls.
I would ask that you look at Chapter 7 of the IBC for reference. There are two sections that may be useful: prescriptive fire resistance rating (Section 721) and calculated fire resistance rating (section 722).
They have a list of assemblies that achieve a fire resistance rating based on different configurations and then they have a method for calculating the fire resistance rating if the assembly is not within Section 721.
https://up.codes/viewer/general/int...pter/7/fire-and-smoke-protection-features#721
Reactions: cda
Welcome PJ
You give some very lucid answers
So how long have you been dealing with codes???