CBC 2016 Section 1028.4.2 - Egress Court

Archana Jain

REGISTERED
Joined
Feb 28, 2017
Messages
3
Location
Santa Clara
I had a question on the egress court as per Section 1028.4.2. If we are exiting from the side of a building which has 6' of setback from the property line, does this section mean that the property wall also needs to be 10' tall and one hour rated? Or just the building wall which will need to be one hour rated for a height of 10' and all openings 45 min rated?

I am unable to attach a dwg to show the condition so writing it clearly.
 
I had a question on the egress court as per Section 1028.4.2. If we are exiting from the side of a building which has 6' of setback from the property line, does this section mean that the property wall also needs to be 10' tall and one hour rated? Or just the building wall which will need to be one hour rated for a height of 10' and all openings 45 min rated?

I am unable to attach a dwg to show the condition so writing it clearly.


Some how if you can change it to a link,
You can post the link

Beyond my computer training
 
All the walls one hour including the property wall under the IBC

1027.4.2 Construction and openings.
Where an egress court serving a building or portion thereof is less than 10 feet (3048 mm) in width, the egress court walls shall have not less than 1-hour fire-resistance-rated construction for a distance of 10 feet (3048 mm) above the floor of the court. Openings within such walls shall be protected by opening protectives having a fire protection rating of not less than 3/4 hour.



COURT. An open, uncovered space, unobstructed to the sky, bounded on three or more sides by exterior building walls or other enclosing devices.
 
All the walls one hour including the property wall under the IBC

1027.4.2 Construction and openings.
Where an egress court serving a building or portion thereof is less than 10 feet (3048 mm) in width, the egress court walls shall have not less than 1-hour fire-resistance-rated construction for a distance of 10 feet (3048 mm) above the floor of the court. Openings within such walls shall be protected by opening protectives having a fire protection rating of not less than 3/4 hour.



COURT. An open, uncovered space, unobstructed to the sky, bounded on three or more sides by exterior building walls or other enclosing devices.
Thank You this helps as this was the main confusion.
 