I am working on a renovation in an existing high rise, type 2A construction, for a local universities downtown campus. The existing floor plan consists of 5 large classrooms and a couple of small offices and a conference room. We are going to be demolishing one of the classroom and the existing offices and making a new office suite with a mix a new offices and conference rooms to support the remaining (4) classrooms. While our project area is only about half the existing floor plate I have calculated the occupant loads of the entire floor (renovated & non-renovated areas) and the total occupant load is 60 people larger than the existing stairs egress capacity as calculated by current Connecticut Building code. I have also calculated the occupant load of the existing floor plan with the (5) classrooms and the occupant load calculates out to be 80 people larger than the existing stairs egress capacity as calculated by current Connecticut Building code.
Is there any leeway in the Existing Building code to make the argument that while the proposed occupant load exceeds the existing stair egress capacity, the new occupant load is lower than the existing occupant load thus making a bad situation better, but still not up to code?