Yikes
I'm seeing a potential conflict between CBC 11B/ADA and the NEC regarding an ADA
mobility accessible kitchen:
- Kitchen is "L" or "U" shaped with standard 25" deep counters. (I typically put 1"
extension boxes on the outlets so that the side reach is 24" deep max per 11B-308.3.2.)
the "L" or "U" creates an inside corner countertop surface that is 25"x25" that cannot
be reached directly in front of the wheelchair.
- NEC 210.52 (C)(1) says: "Wall Countertop Spaces. ...Receptacle outlets shall be
installed so that no point along the wall line is more than 600 mm (24 in.) measured
horizontally from a receptacle outlet in that space." In other words, max 48" spacing
between countertop outlets.
My problem: I make the outlets accessible per ADA/11B at the 25" deep inside
corner, then they would be spaced at least 50" apart, not 48".
To put it another way, the NEC is compelling me to put countertop outlets at a closer
spacing than can be made accessible per ADA/11B for a standard 24-25" inside corner.
Where is the wiggle room to comply with both codes?