Does the public need to have access to the required service sink? It looks like 2009 IPC 403.3 requires all fixtures required by table 403.1 need to be provided for the public and employees.
Not to the service sink, restroom with lav most likely.
And as a heads up, service sink will need to be A117.1 compliant.
TyJ., Can you please provide the Code Sections that
require the Service Sink to be A117.1 compliant & the
edition of the A117.1 you are referencing ?
Thanks !
Rick,
Section 403.3 [ in the `09 IPC ] is for "Required Public Toilet
Facilities".........Service Sinks are not [ typically ] located
within a Public Toilet.
2010 ADASAD 212.3 Sinks.
EXCEPTION:
Mop or service sinks shall not be required to comply with 212.3.
I do believe ANSI 117.1 is quiet on mop utility and service sinks.
2015 IPC- section 1109 - Operable Parts for Service Personnel do not need to be accessible.
If based on the original question, it is accessible by the public, them it would need to be accessible.
Why in the world would you want a service sink available to the public?
It is for service not for the public....
The codes work together, all sections, all volumes, not each section independent of each other.
EXCEPTION:
I do believe ANSI 117.1 is quite on mop utility and service sinks.
Agree that the service sink does not need to be available to the public, that is beside the intent of a service sink. The service sink would be accessible due to the need for employees with disabilities to have equal access.
We would be speaking of the "reasonable accommodation" requirement based on Title I for employees on an as needed basis.
Not going to get into employment laws but:
ADA prohibits employment discrimination against qualified individuals with disabilities.
If one of the requirements of the service person is to climb a ladder to change a bulb/tube, the disabled person is not qualified, and not covered. No reasonable Accommodations required.
2010 ADASAD in section 212.3 Sinks. Clearly states NOT Required.
EXCEPTION:
You beat the horse to death, let it die.
I am not saying anything about accessibility. The 2009 IPC section 403.3 requires all fixtures required by table 403.1 to be provided for the public and employees. Service sinks are in table 403.1. If the service sink is in a locked closet it would not be available to the public or to some employees.
The service sink needs to be available to all tenants, and whoever has a key needs to be accountable for what they dump into the service sink.
EXCEPTION:
QUOTE]
Not everyone uses the ADASAD - locally we follow the IBC and it's references to ICC A117.1-2009