Keith
Member
With less than 49 occupants, Does more than 100' distance to exit trigger requirement for 2 exits? (CBC 1006.2.1) (Sprinklered building - B occupancy)
I have a space with less than 49 occupants, which only requires 1 exit, but distance to the exit is more than 100', so plan checker says more than 100' distance to exit in a sprinklered bldg per 1006.2.1 requires 2 exits.
Any clarifications on this I can share with the plan checker or is he right?
Thanks!
I have a space with less than 49 occupants, which only requires 1 exit, but distance to the exit is more than 100', so plan checker says more than 100' distance to exit in a sprinklered bldg per 1006.2.1 requires 2 exits.
Any clarifications on this I can share with the plan checker or is he right?
Thanks!