I'm working on a 7-story residential apartment building. The owner has just decided to increase the size of the level 07 indoor / outdoor amenity space and I am wondering if there's any way of getting out of the increase in Construction Type required. Previously this space had been under 10% of the gross floor area but with the changes it is over.
The gross floor area of this level is 9,268 (which does not include the uncovered roof deck or tenant private roof decks - floor plate is 12,090). The outdoor area is 1,106 (partly covered) and the indoor area is 1,080 including restrooms and other support spaces. So, it appears we are not close.
The podium is 20'-0" to the top, and Level 07 is at 67'. These are measured to our level 01 finish floor, so we probably have to add about a foot to grade plane, which slopes down from level 01.
We're planning a podium approach based on 510.2. The podium is a concrete structure with PT slab at top. The building above the podium is CFMF bearing walls and metal stud construction throughout. Concrete composite slab on open web steel joists.
We are fully sprinkelered.
So we now have an A-3, non-accessory space at the highest occupied floor of the building. Per 504.2, we have to comply with the height and story limits for each occupancy.
We comply for R-2 (limited to 5 stories above podium, and would comply with Types IIA or B (85' and 75' respectively). The A-3 building complies in height (75' & 85' for Type II), but not in stories (4 max for IIA).
If we have to go to IB, we're adding significant expense and complexity.
Is there any exception or other approach that could get me out of this?
Thank you
I'm working on a 7-story residential apartment building. The owner has just decided to increase the size of the level 07 indoor / outdoor amenity space and I am wondering if there's any way of getting out of the increase in Construction Type required. Previously this space had been under 10% of the gross floor area but with the changes it is over.
The gross floor area of this level is 9,268 (which does not include the uncovered roof deck or tenant private roof decks - floor plate is 12,090). The outdoor area is 1,106 (partly covered) and the indoor area is 1,080 including restrooms and other support spaces. So, it appears we are not close.
The podium is 20'-0" to the top, and Level 07 is at 67'. These are measured to our level 01 finish floor, so we probably have to add about a foot to grade plane, which slopes down from level 01.
We're planning a podium approach based on 510.2. The podium is a concrete structure with PT slab at top. The building above the podium is CFMF bearing walls and metal stud construction throughout. Concrete composite slab on open web steel joists.
We are fully sprinkelered.
So we now have an A-3, non-accessory space at the highest occupied floor of the building. Per 504.2, we have to comply with the height and story limits for each occupancy.
We comply for R-2 (limited to 5 stories above podium, and would comply with Types IIA or B (85' and 75' respectively). The A-3 building complies in height (75' & 85' for Type II), but not in stories (4 max for IIA).
If we have to go to IB, we're adding significant expense and complexity.
Is there any exception or other approach that could get me out of this?
Thank you