• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Filter Requirements for Apartment HVAC

ADAguy

Registered User
Joined
Sep 11, 2013
Messages
6,307
Location
California
Code minimum vs mold prevention vs regular maintenance for habitability?
Landlords duty to maintain?
Life expectancy to ducted split system with roof mounted condenser and RA in ceiling soffit.
If all windows are kept close where does Makeup air/RA come from?
 
$ ~ $ ~ $

ADAguy,

Lot's of questions in your OP......What are you trying to determine first ?
Also, you did not mention anything about your Supply Air.


$ ~ $ ~ $
 
Filters depend on lease agreement

Make up air? Apartments not that tight

Newer ones I see it brought in from outside.
 
I don't understand the question(s)??

HVAC systems typically have filters. Who changes it depends on what the lease says, but it is ultimately the owners' responsibility. The manufacturer of the HVAC unit will provide instruction regarding filter type and size, supply / makeup / exhaust air requirements, venting requirements, etc. Life expectancy is short, like everything these days - if you get 15 years out of a new install, be happy. If there is mold, it is likely more a problem with the structure itself than the HVAC system, at least in my climate - I don't know if you sunshine guys have different considerations there.

An aside - I would think mold should be pretty rare in CA, no? Or at least in Southern CA? How locked up tight would you have to have a place to grow mold where it doesn't rain and there's no humidity?
 
Yes, split system; Condenser on roof with furnace fan in a hallway soffit. It appears that exposed copper piping above return air filter door is sweating due to temp differential. Blower fan blades are collecting dust. Lab test indicates presence of some air borne particulates and mold spores. No visible mold spores on walls but an odor is noticeable.
 
Is it one of those off-the-shelf $10 lab test kits? Like Pro-Lab or something? I don't trust those much. There are mold spores present in virtually every bit of air on the planet - that $10 kit is always going to test positive for "mold". Just my opinion, but I wouldn't put any faith in those things if that's what you used.

There's also dust pretty much everywhere. Spinning fan + moving air = accumulation of dust on fan. Clean fan periodically to make it go away.

If you have condensation on a pipe, maybe try putting a piece of pipe insulation on it?
 
Is the mold test a qualitative test or quantitative test?

I've been told that heat pumps need to be cleaned once to twice a year by a certified professional.
 
no JC, an actual person from a lab came an took samples, did an analysis and bingo. Tenant is experiencing health issues from breathing the air, she has lived in the unit for 14 years. Only started to experience issues this year.
Same building owner/manager.
 
That makes more sense, and is (again, in my opinion) a much bigger red flag than a store bought test.

It seems odd that condensation on a pipe could cause enough of a problem to lead to those issues, though, especially if there is no visible evidence of the mold. Is the house on a slab, or a crawlspace/basement? Have you looked in the attic? Can you get an HVAC company to send a camera down/through the ductwork?
 
JC, 3 story apartment building (built 2004), tenant on 3rd floor. Some green growth on exterior plaster at condensate drain.
Temp extremes from 72 to 111 during hottest periods.
Ducts have been "partially" cleaned but tech not very professional.
 
# ~ # ~ #

ADAguy,

When the lab took samples, what was actually sampled ?
The air only, ...walls, ...inside the ducting, other ?.....Point
being that it may not be just the HVAC......Could there be
leaks in the roofing system, ...draining down inside the
walls ?.....We have this very scenario at one of our facilities.
Possibly mold, but definitely mildew is present most
everywhere on the interior......We are researching exact
locations trying to pinpoint the source of the water intrusion.
Water in the walls is leaching thru to the interior.

Is the HVAC system in your application balanced, ...air
filters being changed regularly ?......I have been told that
clogged, dirty air filters is the number one cause of most
HVAC system problems [ i.e. - who knows what all is living
and breeding in clogged, rarely changed air filters ].


# ~ # ~ #
 
no JC, an actual person from a lab came an took samples, did an analysis and bingo. Tenant is experiencing health issues from breathing the air, she has lived in the unit for 14 years. Only started to experience issues this year.
Same building owner/manager.


Did they happen to sample other apartments.
 
I have seen people live in the same unit for years

Sometimes it is a pretty site,,

A lot of times not very nice to be in.
 
I am thinking

If the tenant has been complaining for a long time and manager has not done anything,,,

Problem

If recently notified or manager has been trying to resolve the problem

Than no problem

Plus if recently manager has right to try to resolve the issue.
 
CDA:
1. Tenant has complained, management has been slow to respond or response has not been adequate. This has been going on for over a year. Attorney now involved.
2. High end property
3. City of LA has a regular program for inspection of units but does not do air tests
North:
1. No, no other units tested
2. Filters only changed annually with code min. filters.
3. HVAC Unit is 14 years old, at end of useful life?
4. Fix appears simple but owner doesn't want to expend the money as he would probably have to replace all units (13) in building.
 
Mold is tricky. And just because she is sick and has a Dr. telling her it's because of mold, is the "expert witness" Dr. that the building owner hires during the trial going to say the same thing? And how do you know the mold that's causing her problems is from that building? Could it not be from work, or from a public place, or any other structure she regularly frequents? Does she have bad health habits that could exacerbate a problem that maybe wouldn't effect anyone else? Etc etc etc...

Not trying to be discouraging, but I've seen this movie before. Unless there's a very obvious, well documented, independently verified case of severe mold within her unit, she's going to have a hard time winning any battles in court. Especially if no one else in the building has any issues.
 
JC, thank you for your comments, many are similar concerns as mine. It may come down to who has deeper pockets but if I was the owner/landlord I would make the necessary repairs as he has a good tenant and could create ill-will among the other tenants.
 
Top