jar546
Forum Coordinator
You have a large, custom home with an 800A UG service to an MDP with the following overcurrent devices:
Service Disconnect 800A 120/240 Single Phase
Then
60A Dbl Pole to a dock
100A Dbl Pole to a dock
20A Dbl Pole to a boat lift
60A Dbl Pole to an equipment panel
20A Single Pole to a generator battery charger
100A Dbl Pole to another equipment panel
200A Dbl Pole to panel A
200A Dbl Pole to panel B
200A Dbl Pole to Panel C
200A Dbl Pole to a dock
The generator has a 200A CB and rated at approximately 48KW
There are already 2 ATS' (automatic transfer switch) in place, each rated for 200A
The homeowner plans on having an electrician add another 200A transfer switch for one of the 200A panels currently not on the generator power.
There is no plan for load shedding and the current setup lacks any type of load shedding.
What information would you request in order to approve this installation so you could perform an inspection?
Service Disconnect 800A 120/240 Single Phase
Then
60A Dbl Pole to a dock
100A Dbl Pole to a dock
20A Dbl Pole to a boat lift
60A Dbl Pole to an equipment panel
20A Single Pole to a generator battery charger
100A Dbl Pole to another equipment panel
200A Dbl Pole to panel A
200A Dbl Pole to panel B
200A Dbl Pole to Panel C
200A Dbl Pole to a dock
The generator has a 200A CB and rated at approximately 48KW
There are already 2 ATS' (automatic transfer switch) in place, each rated for 200A
The homeowner plans on having an electrician add another 200A transfer switch for one of the 200A panels currently not on the generator power.
There is no plan for load shedding and the current setup lacks any type of load shedding.
What information would you request in order to approve this installation so you could perform an inspection?