If a house has 4 bathrooms and the electrician runs a 20A circuit to feed all 4 bathroom receptacles only, is that code compliant? I am talking about required circuits, not GFCI protection or anything else.
Your premier resource for building code knowledge.
This forum remains free to the public thanks to the generous support of our Sawhorse Members and Corporate Sponsors. Their contributions help keep this community thriving and accessible.
Want enhanced access to expert discussions and exclusive features? Learn more about the benefits here.
Ready to upgrade? Log in and upgrade now.
210.11(C)(3) Bathroom Branch Circuits.
In addition to the number of branch circuits required by other parts of this section, at least one 120-volt, 20-ampere branch circuit shall be provided to supply a bathroom receptacle outlet(s). Such circuits shall have no other outlets.
Exception: Where the 20-ampere circuit supplies a single bathroom, outlets for other equipment within the same bathroom shall be permitted to be supplied in accordance with 210.23(A)(1) and (A)(2).
Nice! Do you have an answer to share?
Also, I assume you have a PDF of the NEC? Where and how much?
1000 W? Most of the newer hairdryers are at least 1500 if not 1800 W.Yes, code-compliant. Bad idea though. A hair dryer probably draws about 1000 watts (8.3 amps). Two bathrooms with two teenage girls could easily mean two blowdryers plus a curling iron or two running at the same time. Permissible, but bad practice, in my opinion.