Service Panel for Mobile Home Violations

Since no one else that participates in this forum ever does any electrical inspections other than ICE and I, I will list the 3 violations:

1) The panel neutral/ground bar is not bonded to the panel. The bond screw is missing on the top.

2) The PVC nipple that feeds the back of the panel from the meter base is missing (wire size #4 or larger)

3) The top neutral lug is improperly installed and not listed to be used that way. They are using the mounting screw to mount the lug on top of the bar.

So what are those NEC code section (or IRC)?
 
Since no one else that participates in this forum ever does any electrical inspections other than ICE and I

That is incorrect. There are a few sharp electrical inspectors. In case you haven't noticed, nobody gets excited about looking up code sections. Perhaps you could provide the sections and that would encourage the participants to look at the code book.

I know that you said that this is new work but the breakers look old....too old....can't even identify the pair on the right. The wiring seems odd but I can't tell from the picture.....what do the breakers on the right serve?

There's something wrong about the white wire that has been relabeled green.

Is the wire from the top 50amp on the left crossing over the line bus? Definitely too short..too short..definitletly too short....Judge Wapner comes on in fifteen minutes.
 
Last edited:
Jeeze, you sound like my boss. "Am I the only one who does any inspections around here?"
Just kidding.

I believe the code references you are looking for are:
#1) 250.24(B)
#2) 300.4(G) and 352.46
#3) 110.3(B)

The absence of a grounding electrode conductor should be addressed.
 
Looking 'outside the box', might need to make sure the service equipment is within 30' of the exterior wall of the mobile home. 550.32(A)
 
Jeeze, you sound like my boss. "Am I the only one who does any inspections around here?"
Just kidding.

I believe the code references you are looking for are:
#1) 250.24(B)
#2) 300.4(G) and 352.46
#3) 110.3(B)

The absence of a grounding electrode conductor should be addressed.

Thank you for taking the time to list those items. I am trying to build up the electrical section here to increase membership. Also, no need to look outside the box here, I was keeping this as a what you see is what you get. The GEC was fine with 2 rods btw.
 
My question pertained to the KO punched out on the back of the panel above the lugs, it looks like a PVC TA with a lock nut to me & also needs a bushing as the conductors look larger then 6 AWG.
 