Based on the underlined passages below, I would interpret that a combination Hi/Lo drinking fountain is a single plumbing fixture. If your project plumbing calculations based on occupant load require two drinking fountains , than a combination Hi/Lo fixture would only count as one of the two required fixtures. Or you could put in a separate Hi and separate Lo fixtures and be compliant with both 1109.5.1 and your plumbing calculations.
1109.5.1 Minimum number.
No fewer than two drinking fountains shall be provided. One drinking fountain shall comply with the requirements for people who use a wheel-chair and one drinking fountain shall comply with the requirements for standing persons.
Exceptions:
1. A single drinking fountain with two separate spouts that complies with the requirements for people who use a wheelchair and standing persons shall be permitted to be substituted for two separate drinking fountains.
1109.5.1 Minimum number.
No fewer than two drinking fountains shall be provided. One drinking fountain shall comply with the requirements for people who use a wheel-chair and one drinking fountain shall comply with the requirements for standing persons.
Exceptions:
1. A single drinking fountain with two separate spouts that complies with the requirements for people who use a wheelchair and standing persons shall be permitted to be substituted for two separate drinking fountains.