Let's break this down:
408.41 Grounded Conductor Terminations. Each grounded
conductor shall terminate within the panelboard in an individual
terminal that is not also used for another conductor.
Exception: Grounded conductors of circuits with parallel conductors
shall be permitted to terminate in a single terminal if the terminal is
identified for connection of more than one conductor.
This means that unless you are connecting parallel neutrals, you cannot put 2 neutrals under one lug, even if the lug is listed for 2 conductors of the size you are attaching.
408.41 Grounded Conductor Terminations. Each grounded
conductor shall terminate within the panelboard in an individual
terminal that is not also used for another conductor.
Exception: Grounded conductors of circuits with parallel conductors
shall be permitted to terminate in a single terminal if the terminal is
identified for connection of more than one conductor.
This means that unless you are connecting parallel neutrals, you cannot put 2 neutrals under one lug, even if the lug is listed for 2 conductors of the size you are attaching.