mtlogcabin
SAWHORSE
Both the ICC and IAPMO mechanical and plumbing codes have similar language for protection of non steel piping when the pipe is less than 1.5 inches from the nearest edge of the framing member. Does any know of similar language for the protection of plastic sprinkler piping? I have search NFPA, Manufacturers installation instructions, ESR report and I cannot find a requirement?
305.5 Protection against physical damage.
In concealed locations where piping, other than cast-iron or steel, is installed through holes or notches in studs, joists, rafters or similar members less than 11/2 inches (38 mm) from the nearest edge of the member, the pipe shall be protected by shield plates. Protective steel shield plates having a minimum thickness of 0.0575 inch (1.463 mm) (No. 16 gage) shall cover the area of the pipe where the member is notched or bored, and shall extend a minimum of 2 inches (51 mm) above sole plates and below top plates.
305.5 Protection against physical damage.
In concealed locations where piping, other than cast-iron or steel, is installed through holes or notches in studs, joists, rafters or similar members less than 11/2 inches (38 mm) from the nearest edge of the member, the pipe shall be protected by shield plates. Protective steel shield plates having a minimum thickness of 0.0575 inch (1.463 mm) (No. 16 gage) shall cover the area of the pipe where the member is notched or bored, and shall extend a minimum of 2 inches (51 mm) above sole plates and below top plates.