when do yo expect to change the cable as is rots out
ACI 318 concrete code which is the IBC reference code and would cover most jurisdictions.
There are a number of requirements including min. 1.5" cover for conduits exposed to earth or weather, and 3/4" cover for concrete not exposed to weather or in contact with the ground.
Conduit should not be more than 1/3rd slab thickness.
Aluminum reacts with the alkalis (OH) found in portland cement concrete. When these two chemicals are combined, the reaction produces hydrogen gas. Serious consequences can arise in situations of long-term contact.
Years ago PCA issued two reports on the subject: Corrosion of Aluminum Conduit in Concrete (RX173) and Corrosion of Embedded Material Other Than Reinforcing Steel (RX198).
You'll find summaries of these reports at www.cement.org
It appears as if the sole plate is missing.......Also,
no protection \ guards for the vertical electrical conduit
in the wall, where a sole plate would typically be.
You DID catch this didn't you Mr. Electrical Inspector ?
ACI 318 does cover embedded steel and plastics in concrete.You cannot get to ACI 318 from the IBC in this instance because there are no electrical requirements in the IBC. [A] 102.4 Referenced codes and standards. The codes and standards referenced in this code shall be considered part of the requirements of this code to the prescribed extent of each such reference and as further regulated in Sections 102.4.1 and 102.4.2.
No reference to ACI 318 in Part VIII of the IRC.
Chapter 4 is "Foundations". It's a stretch IMHO to apply this to an interior slab.
R402.2 deals with resistance to freeze/thaw and chemical resistance.
R402.2 Concrete.
Concrete shall have a minimum specified compressive strength of f c, as shown in Table R402.2. Concrete subject to
moderate or severe weathering as indicated in Table R301.2(1) shall be air entrained as specified in Table R402.2. The
maximum weight of fly ash, other pozzolans, silica fume, slag or blended cements that is included in concrete mixtures
for garage floor slabs and for exterior porches, carport slabs and steps that will be exposed to deicing chemicals shall
not exceed the percentages of the total weight of cementitious materials specified in Section 19.3.3.4 of ACI 318.
Materials used to produce concrete and testing thereof shall comply with the applicable standards listed in Chapters 19
and 20 of ACI 318 or ACI 332.
ACI 318 Chapter 19 deals with the composition of the concrete itself including the percentages of fly ash and slag.
Chapter 20
20.1—Scope
20.1.1 This chapter shall apply to steel reinforcement, and shall govern (a) through (c):
(a) Material properties
(b) Properties to be used for design
(c) Durability requirements, including minimum specified cover requirements
Chapter 26 (Not referenced in R402.2)
26.8.2(f) Conduit and piping shall be fabricated and installed so that cutting, bending, or displacement of reinforcement
from its specified location is not required.
But it doesn't...To say that ACI 318 does not apply to this question reflects a lack of understanding of ACI 318.
Where I am from, Texas, any service buried in concrete, for a kitchen island in this example, is required per the 2017 Electrical Code to be encased in MC cable with a covering such as PVC plus be placed in a schedule 40 conduit plus be buried at least with 2 inches of concrete above the conduit. MCAC is not required, just MC. This is not an interpretation. My daughter is building a home and I caught this and spoke with the investigator from the TDLR and he cited the regs. There is no exception. The ele. contractor just screwed up. Do it right the first time and there are no problems later. Quit cutting corners.You see this for the future island during an remodel. What comments will you have on your inspection report?
Welcome and thank you for participating in this thread.Where I am from, Texas, any service buried in concrete, for a kitchen island in this example, is required per the 2017 Electrical Code to be encased in MC cable with a covering such as PVC plus be placed in a schedule 40 conduit plus be buried at least with 2 inches of concrete above the conduit. MCAC is not required, just MC. This is not an interpretation. My daughter is building a home and I caught this and spoke with the investigator from the TDLR and he cited the regs. There is no exception. The ele. contractor just screwed up. Do it right the first time and there are no problems later. Quit cutting corners.