• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

What's Wrong with this Diagram?

jar546

Forum Coordinator
Joined
Oct 16, 2009
Messages
11,028
Location
Somewhere Too Hot & Humid
This is an easy one. There is essentially one major thing in NEC 250 that is completely wrong. You may find more but I stopped when I saw this one thing.
Screen Shot 2019-08-15 at 18.38.17.png
 
This took longer than I thought it would. I kept wondering why we were upsizing one of the sets of feeders to 125 amps, and I couldn't understand.
 
Sorry, I didn't finish my thought. NEC 250.24(A) requires the grounding electrode conductor to be connected to the grounded service conductor at the service, not in a sub-panel.
 