Mr. Inspector
2015 IBC table 1108.2.7.1. How do you calculate the amount of receivers for assistive listening systems that are required in assembly areas that have audible communications if there are no permanent seats or no seats at all?
# of occupants allowed in space.
This is a gym with a 100 occupants. So your saying that they need 100 receivers? Is that in the ADA?
I need something from the 2015 IBC. They will a a few benches along the walls that are not fixed.
IBC
Are you sure audible communications is integral to the use of this space"
TABLE 1108.2.7.1
RECEIVERS FOR ASSISTIVE LISTENING SYSTEMS
1108.2.7 Assistive listening systems.
Each building, room or space used for assembly purposes where audible communications are integral to the use of the space shall have an assistive listening system.
Exception: Other than in courtrooms, an assistive listening system is not required where there is no audio amplification system.
1108.2.7.1 Receivers.
Receivers shall be provided for assistive listening systems in accordance with Table 1108.2
Is that IBC or ADA?No it is 5% or 1 min.
Rick, not a code guy or B.O.?
I am an inspector/plans reviewer for building, accessibility and more.
Looks like mtlogcabin post of the ADA defines the term "assembly" different than the IBC. All the spaces that the ADA is calling assembly would need to have over 50 occupants to be called assembly in the IBC (section 303.1.1). Except for classrooms which would be "Educational Group E" no matter how may occupants. I don't enforce ADA only the IBC.
2015 IBC 301.1 Scope. The provisions of this chapter shall control the classification of all buildings and structures as to use and occupancy.
The gym I am looking at is not on a school so It's "Assembly Group A-3 per IBC section 303.4. I don't see where it says school Gym would be "Educational Group E".
Thanks Yikes. I think I need to add what you said on the plans to the C. O.