Have you ever come across a plastic washer box in a 1-hr rated wall?
And have you ever seen a plastic washer box in the same cavity for the other apartment?
Looking for the code that prevents this?
Trying to figure out which edition this is out of
IBC 711.3.2:
1. Steel boxes that do not exceed 16 square inches (4” x 4”) may be installed provided the total area of openings does not exceed 100 square inches for any 100 square feet of wall area.
2. Boxes on opposite sides of a wall shall be separated as follows:
a. By a horizontal distance of not less than 24”.
b. By a horizontal distance not less than the depth of the wall cavity where the wall cavity is filled with cellulose loose-fill or mineral fiber insulation. (Not standard fiberglass insulation)
c. By solid fire-blocking complying with section 716.2.1. (Not practical for back to back boxes)
d. By other listed materials and methods. (This would include fire stop pads inside boxes or outside that covered all 5 exposed sides)
3. Listed box assemblies that have been tested for use in fire rated assemblies can be used in accordance with their listing and instructions.
The plumber is going to install rated boxes, but I requested they should not be in the same cavity, he was looking for a way around the distance requirement. The building had plastic boxes back to back
Thanks for the information
You did not say remodel,,,
Did they take all the Sheetrock down??
Or what was kind of the scope of work?
Gotcha....that will be determined by the specific listing of the box being installed. Most will not permit back to back installation
Ty J's link to souixchief shows their rated intumescent boxes installed side by side against a metal stud that has openings in the stud, and a double stud assembly, effectively one large cavity. It would be easiest for the contractor to purchase these fire-rated boxes.
I won't use the requirements for electrical boxes in this case because these are not electrical boxes and therefore that section of the code does not apply.
it is membrane penetrations:::
Not just electrical
714.3.2 Membrane Penetrations
Membrane penetrations shall comply with Section 714.3.1. Where walls or partitions are required to have a fire-resistance rating, recessed fixtures shall be installed such that the required fire-resistance will not be reduced.
  1. Membrane penetrations of maximum 2-hour fire-resistance-rated walls and partitions by steel electrical boxes that do not exceed 16 square inches (0.0 103 m2) in area, provided the aggregate area of the openings through the membrane does not exceed 100 square inches (0.0645 m2) in any 100 square feet (9.29 m2) of wall area. The annular space between the wall membrane and the box shall not exceed 1/8 inch (3.2 mm). Such boxes on opposite sides of the wall or partition shall be separated by one of the following:
    1. By a horizontal distance of not less than 24 inches (610 mm) where the wall or partition is constructed with individual noncommunicating stud cavities;
    2. By a horizontal distance of not less than the depth of the wall cavity where the wall cavity is filled with cellulose loosefill, rockwool or slag mineral wool insulation;
    3. By solid fireblocking in accordance with Section 718.2.1;
    4. By protecting both outlet boxes with listed putty pads; or
    5. By other listed materials and methods.
  2. Membrane penetrations by listed electrical boxes of any material, provided such boxes have been tested for use in fire-resistance-rated assemblies and are installed in accordance with the instructions included in the listing. The annular space between the wall membrane and the box shall not exceed 1/8 inch (3.2 mm) unless listed otherwise. Such boxes on opposite sides of the wall or partition shall be separated by one of the following:
    1. By the horizontal distance specified in the listing of the electrical boxes;
    2. By solid fireblocking in accordance with Section 718.2.1;
    3. By protecting both boxes with listed putty pads; or
    4. By other listed materials and methods.
  3. Membrane penetrations by electrical boxes of any size or type, that have been listed as part of a wall opening protective material system for use in fire-resistance-rated assemblies and are installed in accordance with the instructions included in the listing.
  4. Membrane penetrations by boxes other than electrical boxes, provided such penetrating items and the annular space between the wall membrane and the box, are protected by an approved membrane penetration firestop system installed as tested in accordance with ASTM E814 or UL 1479, with a minimum positive pressure differential of 0.01 inch (2.49 Pa) of water, and shall have an F and T rating of not less than the required fire-resistance rating of the wall penetrated and be installed in accordance with their listing.
  5. The annular space created by the penetration of an automatic sprinkler, provided it is covered by a metal escutcheon plate.
  6. Membrane penetrations of maximum 2-hour fire-resistance-rated walls and partitions by steel electrical boxes that exceed 16 square inches (0.0 103 m2) in area, or steel electrical boxes of any size having an aggregate area through the membrane exceeding 100 square inches (0.0645 m2) in any 100 square feet (9.29 m2) of wall area, provided such penetrating items are protected by listed putty pads or other listed materials and methods, and installed in accordance with the listing.
What is the applicable Code that is being used
to rebuild after the fire ?........IBC, ..IRC, ..IEBC
or something else ?
Can they use mineral wool to pack around the
fire rated Washer Boxes ?........That [ may ] add
to the fire rating and cover the STC.
At least one manufacturer seems to cover both
the fire rating and the STC..........Check out the
Link to Rockwool:
https://www.rockwool.com/
north star,
IBC, group R-2
Yes, rockwool is an option, I'm pretty sure there's an STC rated wall with mineral wool in the cavity, not just around the washer box but the whole wall between units.
Mineral wool would be different than what was there and could create an insurance question or two as to whats the minimum code requirement. If over the minimum, the insurance company may not foot the bill.