So recently a metal fabricator of on our site decided to change the intermediate handrail detail during an install on a set of egress stairs (see detail attached). To me this feels wrong but I haven't really been able to find anything in IBC or ADA that really addresses what I think is an issue. As a person is using the the handrail they have to step off the final tread onto the landing and the height changes. If an extension is required on the side handrails for one tread length, then using that same spirit of the code, this doesn't seem appropriate. Since it's continuous, maybe it doesn't need to extend out a full tread, but the change in height during the step down seems wrong. The only bit of ADA that seems to support this idea is from section 505.4 stating, "Handrails shall be at a consistent height above walking surfaces, stair nosings, and ramp surfaces". Technically it is at a consistent height across the stair nosing but then immediately drops. I feel it should be a consistent height for a bit past the stair nosing into the landing. Anyways, anyone have any thoughts or insights into this?
Handrail Detail
Welcome to the forum.
First lets start with what is shown is a very common and highly used inside turn continuous handrail transition.
Secondly, the reason it is done this way is because many of the architects and designers don't design the stairways large enough to allow for an extra tread depth on the landing at the top and the bottom of stair flights.
In an effort to reduce the size of the exit enclosure, many, I would say a good majority of the designers shove the minimum amount of treads need with the minimum amount of landing needed and can care less about how the handrails flow.
Because there is not enough run out room to flow down at the same angle, the fabricator has to pick a point where they need to make the harsh drop for the height change.  These are always shown on the shop drawings and no one ever complains till the installation.  The height change at the riser is less out of the way than putting it at the corner with the large vertical drop.
If the design firm had added one tread depth on the landing before the required minimum landing depth, the handrail could flow to a level turn point, wrap around and then descend down the next flight.
This same condition occurs at the top of many stair flights when the handrails are not continuous and extensions are required.
Designers constantly put the top riser right at the same point of the walkway cross traffic flow and then complain that the handrails extend out in to the flow.
IF I sound a little harsh, it's because fabricators have been complaining to designers for over 25 years about this exact issue, and we are always told the stairways are not important we need more floor space.
Not the fabricator - its the designer, its hard to shove a size 12 foot in a size 11 shoe.