This issue comes up every so often - a large building (15 RTUs, to give you a sense of scale) but no kitchen, no hood. Lots of outside air required per code and design. I ask for a Test and Balance report, and the HVAC contractor says... "why do I have to do that, there's no kitchen hood?"
As I read the 2018 IMC, and the 2009 IECC (the two codes in effect in this jurisdiction) - I feel pretty comfortable saying that a TAB is required, UNLESS there is no ventilation air required for the occupancy.
Would you agree? Can you point to a particular section that makes this issue more clear, or that shows I'm off base?
BTW - most HVAC contractors around here answer my request with something along the lines of: "yeah - they were here yesterday for the TAB, I'll get you a copy of the report ASAP."