tbz
So here is a question that has come up on another forum and I thought I would get some opinions here.
This applies to both the IBC and the IRC, but the vast majority of the time this is only seen on IBC projects.
This question is specific to Mid-Landings, and we are defining for this question that a Mid-Landing is only accessible from 2 or more stair flights, NO level walkway access or Ramps, only stair flights!
And I am interested in hearing points on this specific yes or no for flagging or passing.
Thanks for the input everyone - Tom
- You have a stairway with 2 stair flights connected by a "Mid-Landing"
- The guard manufacture has fabricated the guard with a bottom horizontal connecting all the infill together
- The treads at the edges between the bottom of the guard, the face of the riser and the top of each tread forms a triangle that complies with exception 2 of IBC 1015.4, the opening is less than 6 inches, but more than 4 inches. Hence compliant.
- However, the bottom riser of the top flight forms the same triangle from the bottom of the guard, face of the riser and now the "Mid-Landing".
- The "Mid-Landing" is not accessible from anything other than a stair flight,
- The 6" sphere is a long standing exception, specifically allowed because it has been found that the 99% of children have grown large enough for this to be a safe exception on stairs because; again the children have grown to a point to be able to negotiate a stair flight that does not present a significant danger, simply they are to big by now to squirm through the triangular opening.
- Getting to this position on a "Mid-Landing" would require either descending the upper flight or ascending the lower flight, noted again for reference.