JigglyPuff
I have an assisted living facility that will be an I-1 that is going into an existing building (church). This church is a one story building with a basement. I'm trying to find out if the existing windows in the basement need to be egress. This project is in the state of Minnesota.
In the Minnesota Building Code under Section 1030 Emergency Escape and Rescue Openings" it says the following:
"In addition to the means of egress required by this chapter, emergency escape and rescue openings shall be provided in Group R occupancies as follows:"
Basements and sleeping rooms below the fourth story above grade plane shall have at least one exterior emergency escape and rescue opening in accordance with this section. Where basements contain one or more sleeping rooms, emergency escape and rescue openings shall be required in each sleeping room, but shall not be required in adjoining areas of the basement. Such openings shall open directly into a public way or to a yard or court that opens to a public way.
There's no mention of any other occupancies outside of Group R, so I think I found the answer but just wanted some confirmation from others who have worked on I-1 buildings.
- 1.Basements with a ceiling height of less than 80 inches (2032 mm) and not used for purposes other than mechanical equipment or storage shall not be required to have emergency escape and rescue openings.
- 2.Emergency escape and rescue openings are not required from basements or sleeping rooms that have an exit door or exit access door that opens directly into a public way or to a yard, court, or exteriorexit balcony that opens to a public way.
- 3.Basements without habitable spaces and having not more than 200 square feet (18.6 m2) in floor area shall not be required to have emergency escape and rescue openings.
- 4.Emergency escape and rescue openings shall not be required under the following conditions:
- 4.1.The building is equipped throughout with an approved automatic sprinkler system in accordance with Section 903.3.1.1 or 903.3.1.2; and
- 4.2.The means of egress system complies without utilizing the single exit provisions under Section 1006.3.3.
- 5.In other than Group R-3 occupancies, sleeping rooms provided with a door to a fire-resistance-rated corridor having access to two remote exits in opposite directions.
- 6.The emergency escape and rescue opening is permitted to open onto a balcony within an atrium in accordance with the requirements of Section 404, provided the balcony provides access to an exit and the dwelling unit or sleeping unit has a means of egress that is not open to the atrium.
- 7.High-rise buildings in accordance with Section 403.
- 8.Basements in Group R-3 occupancies used only to house mechanical equipment that do not exceed a total floor area of 200 square feet (18.58 m2).