I have attached my site plan here. We intend to build several houses on 1 lot, separated by 4' between houses, this 4' would be an easement. Building Inspector says cannot have windows, unless we have no egress windows and use fire rated windows. The inspector says they are "imagining a line in between these buildings, which would be 2' on either side, they are saying they draw it down the middle. These houses will be in a condo regime, with a horizontal property regime. I am under the impression, I measure from one of the walls over to the other building which is 4' which clears me.... I can't seem to get past this issue....
FIRE SEPARATION DISTANCE. The distance measured from the building face to one of the following:
1. To the closest interior lot line; or
2. To the centerline of a street, an alley or public way; or
3. To an imaginary line between two buildings on the lot.
R302.1 Exterior walls.
FIRE SEPARATION DISTANCE. The distance measured from the building face to one of the following:
1. To the closest interior lot line; or
2. To the centerline of a street, an alley or public way; or
3. To an imaginary line between two buildings on the lot.
R302.1 Exterior walls.