Is every floor in a multistory building (3-4 stories) considered a "Fire area", and should all floors be separated from adjacent floors per IBC table 707.3.10 ?
Your premier resource for building code knowledge.
This forum remains free to the public thanks to the generous support of our Sawhorse Members and Corporate Sponsors. Their contributions help keep this community thriving and accessible.
Want enhanced access to expert discussions and exclusive features? Learn more about the benefits here.
Ready to upgrade? Log in and upgrade now.
I thought at that point when i reach the cumulative sq. ft. threshold I need a firewall ? Creating a separate buildingNo, separation would be when you hit the cumulative sq ft threshold.
Now if you are separating occupancies, then that's another story.
So, you would only ever use fire areas to limit the requirements for fire protection (sprinkler system ) ?Fire areas are limited in Section 903 of the building code depending on the occupancy type.
Separate buildings requiring a fire wall would come under Chapter 5 when you exceed the allowable area based on occupancy and construction type.
Thank you !! Much appreciatedPretty much that is what the code allows.
Similar to the Legacy Codes that required "Area Separation Walls" to compartmentalize buildings using a passive system to reduce and slow down the spread of fire.
A fire area separation will usually require a higher hourly fire rating than an occupancy fire separation requirement