I called my local building code office and am having a disagreement about whether or not the battery storage system I am planning would be considered hazardous (H).
They are saying it would be considered hazardous under IFC Chapter 12 because the batteries contain lithium, which is flammable.
However if you look at 1206.2.9 it states that lithium based battery systems will be considered hazardous if they exceed 600 kWh.
My system will be only 128kWh, which is under the limit.
Why would the IFC contain such a limit for lithium batteries if any amount of lithium batteries is going to be treated as Hazardous?
I don't think MT has seen a lot of these battery storage systems yet, so I'm skeptical of their office's interpretation.
In case more details are needed, here is my plan for the building: I believe S2 is the appropriate occupancy type for this building. It has a battery storage room, parking garage, laundry, bathroom, and nonflammable storage room. My interpretation was that nothing in IFC Chapter 12 prevents me from using S2 as long as I am complying with sprinkler system, fire wall, burn ratings etc.
Does anyone know what is the correct interpretation of the code? Can I use S2?
Thanks!
They are saying it would be considered hazardous under IFC Chapter 12 because the batteries contain lithium, which is flammable.
However if you look at 1206.2.9 it states that lithium based battery systems will be considered hazardous if they exceed 600 kWh.
My system will be only 128kWh, which is under the limit.
Why would the IFC contain such a limit for lithium batteries if any amount of lithium batteries is going to be treated as Hazardous?
I don't think MT has seen a lot of these battery storage systems yet, so I'm skeptical of their office's interpretation.
In case more details are needed, here is my plan for the building: I believe S2 is the appropriate occupancy type for this building. It has a battery storage room, parking garage, laundry, bathroom, and nonflammable storage room. My interpretation was that nothing in IFC Chapter 12 prevents me from using S2 as long as I am complying with sprinkler system, fire wall, burn ratings etc.
Does anyone know what is the correct interpretation of the code? Can I use S2?