VLADIMIR LEVIN
Correct me if I'm wrong, but fireplace doors aren't required if you have a tight fitting flue damper?
Depends on which version of the code you are using.Correct me if I'm wrong, but fireplace doors aren't required if you have a tight fitting flue damper?
I didn't think California allowed wood-burning appliances.I just looked at the Residential Code and I did not find a requirement for a door and curiously, no requirement for outside air. Shirley I missed something.
I thought that was only a requirement if the gas logs had a pilot light, I thought if they didn't and the gas had to be turned on manually that wasn't the requirement.Flue dampers are seldom a tight fit and if there is gas plumbed to the fireplace for a gas log the damper requires hardware to prevent a tight fit.
2020 ECCC of NYS R402.4.2- New wood burning fireplaces shall have tight-fitting flue dampers or doors, and outside air combustion.Depends on which version of the code you are using.
2009 IRC
N1102.4.3 Fireplaces. New wood-burning fireplaces shall have gasketed doors and outdoor combustion air.
2012 IRC
N1102.4.2 (R402.4.2) Fireplaces.
New wood-burning fireplaces shall have tight-fitting flue dampers and outdoor combustion air.
2015 IRC
R1006.1 Exterior air.
Factory-built or masonry fireplaces covered in this chapter shall be equipped with an exterior air supply to ensure
proper fuel combustion unless the room is mechanically ventilated and controlled so that the indoor pressure is neutral
or positive.
N1102.4.1.2(R402.4.1.2) Testing.
R1004.5 Gasketed fireplace doors.
A gasketed fireplace door shall not be installed on a factory-built fireplace except where the fireplace system has been
specifically tested, listed and labeled for such use in accordance with UL 127.
New wood-burning fireplaces shall have tight-fitting flue dampers or doors, and outdoor combustion air. Where using
tight-fitting doors on factory-built fireplaces listed and labeled in accordance with UL 127, the doors shall be tested
and listed for the fireplace. Where using tight-fitting doors on masonry fireplaces, the doors shall be listed and labeled
in accordance with UL 907.
Probably in mechanical code and/or energy code. Our Res code doesn't have all that included like the IRC does.I just looked at the Residential Code and I did not find a requirement for a door and curiously, no requirement for outside air. Shirley I missed something.
Fireplaces are allowed to be built but not allowed to be used.....well that depends on the location....here is southern Califoprnia there is an agency named Air Quality Management District. AQMD has rules.I didn't think California allowed wood-burning appliances.
Sounds typical for California!Fireplaces are allowed to be built but not allowed to be used.....well that depends on the location....here is southern Califoprnia there is an agency named Air Quality Management District. AQMD has rules.
AQMD has rules.
Because a lot of people from Cali moved there?...So does Missoula County Montana Health Department believe it or not