This is an open and shut case.Exterior doors may lead to an outside area that will not lead to a public way or a safe dispersal area. Therefore they will not meet the code for an exit in a means of exit system since there is no exit discharge
Your premier resource for building code knowledge.
This forum remains free to the public thanks to the generous support of our Sawhorse Members and Corporate Sponsors. Their contributions help keep this community thriving and accessible.
Want enhanced access to expert discussions and exclusive features? Learn more about the benefits here.
Ready to upgrade? Log in and upgrade now.
This is an open and shut case.Exterior doors may lead to an outside area that will not lead to a public way or a safe dispersal area. Therefore they will not meet the code for an exit in a means of exit system since there is no exit discharge
akelly, welcome to the forum!
It really helps is you tell us (1) where the project is located, so we know which code/jurisdiction is applicable, and (2) whether it is (a) new, (b) existing with no changes, or (c) existing with an addition or alteration proposed.
If you have a space that requires 2 exit doors but has 12 exit doors, then only 2 doors need to be made "code compliant" with the provisions IBC chapter 10 'Means Of Egress'. You certainly would not have exit signs on the other 10 doors if you don't intend to use them for exiting.
Since this was posted in the Accessibility forum, perhaps you meant to ask, "do the other 10 convenience doors in excess of those required by CBC chapter 10 need to be made mobility accessible per CBC chapter 11B?"
Assuming it is in Sacramento or somewhere in California, CBC 11B-206.4.1 for new buildings has a couple of exceptions:
View attachment 8279
ADA is a separate but related issue that you will want to consider as well. It will not be enforced by your city building official.
ADA Standard 206.4.1 says:
View attachment 8280
Let us know if your building is existing - - there may be a different response for existing vs. new.
This post has me considering my current project, a 5000sf existing tenant improvement in California. The building has 7 existing doors but only requires one exit based on 30 or less occupancy. We are making the middle door accessible and the only designated exit for egress, but I've been assuming the other doors can remain as-isakelly, welcome to the forum!
It really helps is you tell us (1) where the project is located, so we know which code/jurisdiction is applicable, and (2) whether it is (a) new, (b) existing with no changes, or (c) existing with an addition or alteration proposed.
If you have a space that requires 2 exit doors but has 12 exit doors, then only 2 doors need to be made "code compliant" with the provisions IBC chapter 10 'Means Of Egress'. You certainly would not have exit signs on the other 10 doors if you don't intend to use them for exiting.
Since this was posted in the Accessibility forum, perhaps you meant to ask, "do the other 10 convenience doors in excess of those required by CBC chapter 10 need to be made mobility accessible per CBC chapter 11B?"
Assuming it is in Sacramento or somewhere in California, CBC 11B-206.4.1 for new buildings has a couple of exceptions:
View attachment 8279
ADA is a separate but related issue that you will want to consider as well. It will not be enforced by your city building official.
ADA Standard 206.4.1 says:
View attachment 8280
Let us know if your building is existing - - there may be a different response for existing vs. new.
Ah, thank you. That exception isn't mentioned in the CBC. But a similar exception is included in the CEBC under alterations.1009.1 Accessible means of egress required. Accessible means of egress shall comply with this section. Accessible spaces shall be provided with not less than one accessible means of egress. Where more than one means of egress are required by Section 1006.2 or 1006.3 from any accessible space, each accessible portion of the space shall be served by not less than two accessible means of egress. Exceptions: 1. Accessible means of egress are not required to be provided in existing buildings.
YCMV....
IIRC the door next to stage was deliberately blocked by the band and one of there crew prevented people from leaving that way. One was through the kitchen and not easily located. The side door out of the bar area - can't recall. And the main entrance was narrow and restricted by ticket counter and a second door for blocking sound. As is predictable, most people tried to exit the way they came in. You go with what you know in an emergency. But it was narrow and cramped and pushing from behind caused people in the door to get jammed. It was hard to imagine a crowd crush - people jammed so tight together they couldn't move - but that has been repeated at a lot of large loos of life assembly events.How did they not find the 4 doors with the lit exit signs but they did find the 2 unlit unmarked ones in a dark nightclub? And one of the required exits was locked at the station nightclub BTW....
I did not give my example a name. Of course in my world all of the egress doors have illuminated exit signs. Why the lemming effect takes hold is not my problem to solve. Providing the bare minimum as required by code is my problem. If nothing else, the Station fire is proof that more can be done to protect life. The Station fire has no bearing on the issue at hand.How did they not find the 4 doors with the lit exit signs but they did find the 2 unlit unmarked ones in a dark nightclub? And one of the required exits was locked at the station nightclub BTW....
Interesting example. I have several theatres with chorus dressing rooms - 10-20 occupants - with doors to exterior. Similar situation. Doors to exterior are compliant with exit sign. Doors from corridor/backstage are not signed and are lockable. I don't know why door from dressing room shouldn't be compliant. You might show me code doesn't require a sign for that number - but the fire marshal will require it 9 times out of 10 - which makes it required as far as I'm concerned.Another example....Exterior door in a private office...now it is a required exit, now we have to add exit signs to get to it...Now you have created a violation of 1016.2 for egress through intervening and you can't lock the office.....
I am not saying we couldn't design stuff better, just saying that it shouldn't have to be "ALL EXTERIOR DOORS"....Common sense has to kick in somewhere...
Where does it say that exits in excess of what is required have to be useable by all building occupants and that no exit door can be from an otherwise locked room?
I don't believe that doors are an amenity, but I certainly would review accessibility to all doors....As part of the circulation path or accessible route...that I believe as an amenity in the space are required to be accesible.
Providing doors that do not meet the same requirements as a “means of egress system” doors Is legal as long as it is not possible to “egress“ through the door. Well then, what is the definition of egress through a door? My conclusion is that egressing a space means exiting that space.A door that leads to a small outdoor dining area for lets say 40 people with no other means of exit is not an exit for the restaurant but it is the exit for the outdoor dinning area.
The door that leads to the outside fenced storage area or play area at a daycare might be an exterior door but not an exit door because the fenced area is not large enough to meet the requirements of a safe dispersal area and you can't get to the public way because of the fence
Doors, gates and turnstiles provided for egress purposes in numbers greater than required by this code shall comply with the requirements of this section.
My position is clear way up - doors to the exterior should be comply with the egress code requirement. It's just simpler, saves time, and makes sense to me. I'm not sure why if it could be an exit that someone wouldnt want it used but yes, fasten shut, paint same as wall, remove hardware. Or put up some furring and cover it. Or do what satisfies officials.So if they had an extra door that they didn't want to be used for egress purposes they should put a "NO EXIT" sign and a padlock on it to prove the door is not provided for egress?
It would be interesting to know what the wording of the code was changed to in your area from IBC 1009.1 which does not required more than 2 accessible means of egress.in my part of texas .. in new construction..any exit door has to be ADA compliant... we often design other doors that could be considered as exit doors but are for function only.. (not ada accessible)... and on those doors we do not put exit signs nor ADA signage... easy to tell which are exits and which are not.