REGISTERED
In this section of 2017 Ohio Building Code. What is the definition of the Exception 2.2? My question is will a fire area of 12,000 sq. ft. that is used exclusively for religious services but uses chairs instead of fixed seating, potential for 450 chairs fall under this exception?
903.2.1.3 Group A-3. An automatic sprinkler system shall be provided for
fire areas containing Group A-3 occupancies and intervening floors of the
building where one of the following conditions exists:
1. The fire area exceeds 12,000 square feet (1115 m2).
Exception:
1.1 Fire areas used exclusively for religious worship services with fixed
seating.
2. The fire area has an occupant load of 300 or more.
Exception:
2.1 Fire areas used primarily for worship with fixed seating.
2.2 Fire areas without fixed seating not used for exhibition or display; or
3. The fire area is located on a floor other than a level of exit discharge
serving such occupancies.
Exception: Areas used exclusively as participant sports areas where
the main floor area is located at the same level as the level of exit
discharge of the main entrance and exit.
903.2.1.3 Group A-3. An automatic sprinkler system shall be provided for
fire areas containing Group A-3 occupancies and intervening floors of the
building where one of the following conditions exists:
1. The fire area exceeds 12,000 square feet (1115 m2).
Exception:
1.1 Fire areas used exclusively for religious worship services with fixed
seating.
2. The fire area has an occupant load of 300 or more.
Exception:
2.1 Fire areas used primarily for worship with fixed seating.
2.2 Fire areas without fixed seating not used for exhibition or display; or
3. The fire area is located on a floor other than a level of exit discharge
serving such occupancies.
Exception: Areas used exclusively as participant sports areas where
the main floor area is located at the same level as the level of exit
discharge of the main entrance and exit.