Is it a code?So ASHRAE 62.2 is not a code but a recommendation to the code?
I do not wish to taint your thoughts or opinion. I am in Ca. which is not where you are, so my words are only to meet a point. The contractor is correct that an exterior exhausted hood is not required, but they must meet all of the other ventilation requirements, ASHRAE, for your specific jurisdiction. If you speak to the code authority, make it a Plan Reviewer or Building Official.Hello Everyone,
Hope you guys can help me out on the building code.
I'm having a house built by a production builder and I asked why my Gas Cooktop has a recirculating range and not a vented one. Their answer was it isn't required in South Carolina. I've asked to pay for it to be vented and they refused. They've told me if you can show it is violating the code they will do it as right now the production builder sub contracts the HVAC and Kitchen Appliances to one supplier. So they just don't wait to pay for it if it's required.
I've been doing some digging for about two weeks and even reached out to the City's inspectors. They pointed me to the IRC 2015
Section M1503 Range Hoods
M1503.1 General
Range hoods shall discharge to the outdoors through a duct. The duct serving the hood shall have a smooth interior surface, shall be air tight, shall be equipped with a back-draft damper and shall be independent of all other exhaust systems. Ducts serving range hoods shall not terminate in an attic or crawl space or areas inside the building.
Exception: Where installed in accordance with the manufacturer's instructions, and where mechanical or natural ventilation is otherwise provided, listed and labeled ductless range hoods shall not be required to discharge to the outdoors.
They are considering a recirculating fan a mechanical ventilation... It's pushing the air back in the room... I find it kind of pointless, the carbon filters will catch some of the grease and bad smell but the Carbon Monoxide, Formaldehyde, and Moisture will just be recirculating in the room.
======> Question 1. Is a recirculating vent acceptable?
M1507.4 Local Exhaust Rates
Local exhaust systems shall be designed to have the capacity to exhaust the minimum air flow rate determined in accordance with Table M1507.4.
TABLE M1507.4
MINIMUM REQUIRED LOCAL EXHAUST RATES FOR ONE- AND TWO-FAMILY DWELLINGS
For SI: 1 cubic foot per minute = 0.0004719 m3/s.
AREA TO BE
EXHAUSTEDEXHAUST RATES Kitchens 100 cfm intermittent or 25 cfm continuous Bathrooms-Toilet
RoomsMechanical exhaust capacity of 50 cfm
intermittent or 20 cfm continuous
======> Question 2. Does this mean it has to be exhausted to the outside?
Thank you in advance![]()
Thank you Ed!I do not wish to taint your thoughts or opinion. I am in Ca. which is not where you are, so my words are only to meet a point. The contractor is correct that an exterior exhausted hood is not required, but they must meet all of the other ventilation requirements, ASHRAE, for your specific jurisdiction. If you speak to the code authority, make it a Plan Reviewer or Building Official.
As a personal thought, outside is the best way to remove cooking odors, you are on the right track!!
You know that there are still people that smoke. Doesn't mean it is healthly.Dare I say millions have been installed without a hood, as have non-vented gas decorative appliances. You are presenting what may be a best practice and a preference. That said, if there is a code, amendment or standard that has been legally adopted that requires hoods then it should be administered for everybody governed by that adoption.
Oh but you do.I dont want to debate this.
Oh but you have.I do not wish to taint your thoughts or opinion.
Exception: Where installed in accordance with the manufacturer's instructions, and where mechanical or natural ventilation is otherwise provided, listed and labeled ductless range hoods shall not be required to discharge to the outdoors.
ICE where does that come from? "Residential range hoods are not required in California."Recirculating residential range hoods are not permitted in California. Residential range hoods are not required in California. In my case the hood exhausts to the exterior and my wife opens a window or two whenever she is cooking on the stove. Her olfactory sensitivity is amazing.
I am with sifu on this. You should hire a contractor to install a vented hood. The builder might object but having no hood is not healthy.
Mechanical ventilation for a kitchen is required but it does not have to be a range hood.ICE where does that come from? "Residential range hoods are not required in California."
Well it is not a prison, so there are windows...lol[RB] VENTILATION. The natural or mechanical process of supplying conditioned or unconditioned air to, or removing such air from, any space.
A recirculating fan does not meet the definition of mechanical ventilation. A window in the kitchen that can be opened meets the definition of natural ventilation. Do you have a kitchen window that can be opened? If yes then the recirculating hood meets code
This is where the builder says, we are building in accordance to the manufacturer's instructions.2018 South Carolina Mechanical Code
505.3 Exhaust Ducts
Domestic cooking exhaust equipment shall discharge to the outdoors through sheet metal ducts constructed of galvanized steel, stainless steel, aluminum or copper. Such ducts shall have smooth inner walls, shall be air tight, shall be equipped with a backdraft damper, and shall be independent of all other exhaust systems. Installations in Group I-1 and I-2 occupancies shall be in accordance with the South Carolina Building Code and Section 904.13 of the South Carolina Fire Code.
Exceptions:
In other than Groups I-1 and I-2, where installed in accordance with the manufacturer's instructions and where mechanical or natural ventilation is otherwise provided in accordance with Chapter 4, listed and labeled ductless range hoods shall not be required to discharge to the outdoors.
Ducts for domestic kitchen cooking appliances equipped with downdraft exhaust systems shall be permitted to be constructed of Schedule 40 PVC pipe and fittings provided that the installation complies with all of the following:
2.1. The duct shall be installed under a concrete slab poured on grade.
2.2. The underfloor trench in which the duct is installed shall be completely backfilled with sand or gravel.
2.3. The PVC duct shall extend not more than 1 inch (25 mm) above the indoor concrete floor surface.
2.4. The PVC duct shall extend not more than 1 inch (25 mm) above grade outside of the building.
2.5. The PVC ducts shall be solvent cemented
Chuck, it is clear that you have your heart set on a (California) hood exhaust that removes the cooking orders to the outside.You know that there are still people that smoke. Doesn't mean it is healthly.
Also did you know there are houses that still have Asbestos! Doesn't mean it's healthy.
I dont want to debate this. It comes down to simple math for me.
Is the chances of getting carbon monoxide poisoning lower when there exhaust is to the outside? Yes. Forget about humidity and all the other issues that are also avoided when the exhaust is vented out.
On a new build, I understand pre production homes want to save every penny but saving on health of the home owner is a very low bar.
Nat Ventilation is the Infiltration that happens when the wind blows or the temp diff that creates the stack effect.What is considered natural ventilation? Anywhere in the code that has clarity ?
Nat Ventilation is the Infiltration that happens when the wind blows or the temp diff that creates the stack effect.
The inside air goes out and is replaced through cracks in the windows and doors or even the building itself.
many people don't realize that a "TIGHT" house has 1/3 of the air in your home exchanged with the outside EVERY HOUR. That is a Tight House. Older homes can be from a little less to more than the entire volumn of your home exchanged with outside EVERY HOUR
You're not living in a submarine, a sealed bottle
Yes, in the 2019 CA Energy code, they are required to have a HERS Rater for a range hood.Mechanical ventilation for a kitchen is required but it does not have to be a range hood.
Note the cliff that California jumped off:
Kitchen range hood fans are now required to be verified by a HERS Rater. The new verification protocol requires comparing the installed model to ratings in the Home Ventilating Institute (HVI) directory of certified ventilation products to confirm the installed range hood is rated to meet the required airflow and sound requirements specified in ASHRAE 62.2. See section 4.6.7 below for more detail. Kitchen range hood fans that exhaust more than 400 CFM at minimum speed are exempt from this requirement.
A HERS Rater for a range hood????? When they finally run out of goofy ideas a day will come when a pile of ashes from a pile of burnt money will be required.
You are required to comply with both the state code and the manufacturer's instructions.Well it is not a prison, so there are windows...lol
It is an open concept, there is only 2 window in the front ( living room ) but non in the back (garage) and none on the side since it is a middle unit. Is there any requirements on where the locations are? Distance and size?
This is where the builder says, we are building in accordance to the manufacturer's instructions.
Chuck, You are correct about the test. I was going to the next step after the Blower door test to the assumptions made to translate the Test value into Natural Air Changes. Of course the actuals are going to be affected by wind and temperature so the Actual / natural value will always change with conditionsNot exactly. The builder does a blow door test after drywall and he told me on the last phase of the identical town homes the middle townhouses got between 0.8-1.75ACH. The outer units are much worse between 2 - 4ACH.
I've also had an inspector there twice and was very picky on the fireblock everywhere and there isn't a vent for the cooktopSo I won't be surprised if I get 0.8 ACH or better. Which is pretty tight.