Schedule 80 where it comes out of the concrete? Treated lumber against the concrete?OK, tit for tat, what about this installation? Schedule 40 pvc, residential pole barn, used as personal woodshop.View attachment 8605
This is refers to NM cable, which cannot be run beneath a slab anyway because any conduit underground is considered a wet location per 300.5(B), and NM cable cannot be used in a wet location.2015 IRC
E3802.3.2 Protection from physical damage. Where
subject to physical damage, cables shall be protected by
rigid metal conduit, intermediate metal conduit, electrical
metallic tubing, Schedule 80 PVC rigid nonmetallic conduit,
or other approved means. Where passing through a
floor, the cable shall be enclosed in rigid metal conduit,
intermediate metal conduit, electrical metallic tubing,
Schedule 80 PVC rigid nonmetallic conduit or other
approved means extending not less than 6 inches (152
mm) above the floor. [334.15(B)]
oes Schedule 40 PVC conduit have to be protected where it leaves the concrete? I can't think of a code section for that off the top of my head.
If I took a wider shot, you will see that the unistrut was properly placed but that too was damaged.Seems that without a couple of simple anchor straps, all the stress was on the fitting that the Cowboy's horse kicked on the Texas Riverwalk
He spent all of his money getting there.Is that under a bridge?
Yes, the side of a bridge which is where the stairwell comes up to.Is that under a bridge? Would vibration be an issue?
Do we know what did the damage? Doesn't ;look like normal wear or tear if they had unistrut supporting the assembly