Realized after that they may just want a squarish ISA on the floor to designate the seating as accessible, but I've never seen anyone require it.I am not even sure what a 2?x30 clear space is supposed to provide at the (assumed?) dining surface, marked or not.
Mark, I think his question is: where is the 4"x4" ISA symbol "permanent placard" required by code?2019 CBC 11B-221 Assembly Areas
11B-221.1 General
Assembly areas shall provide wheelchair spaces, companion seats, designated aisle seats and semi-ambulant seats complying with Sections 11B-221 and 11B-802. In addition, lawn seating shall comply with Section 11B-221.5.
11B-221.2 Wheelchair Spaces
Wheelchair spaces complying with Section 11B-221.2 shall be provided in assembly areas with fixed seating.
Note: When required wheelchair spaces are not occupied by persons eligible for those spaces, individual, removable seats may be placed in those spaces.
11B-221.2.1 Number and Location
Wheelchair spaces shall be provided complying with Section 11B-221.2.1.
Maybe it’s common sense … to keep the restaurant staff from placing a chair there, and to make it obvious that the restaurant has a dedicated HC space.where is the 4"x4" ISA symbol "permanent placard" required by code?
How do you "designate" (per Code) something without identifying it to the end users and "regulators". You can callout all kinds of stuff on the plans, how is the guy/girl making $8 bucks an hour going to know that?Mark, I think his question is: where is the 4"x4" ISA symbol "permanent placard" required by code?
In the sections you quoted above, the only place I see "identification" signage is in 802.4.2 for "designated aisle seats"
The original post was not about the operators of the facility. It was about a building inspector writing a "correction" for which there is no code citation to indicate a violation.How do you "designate" (per Code) something without identifying it to the end users and "regulators". You can callout all kinds of stuff on the plans, how is the guy/girl making $8 bucks an hour going to know that?
That happens a lot more than people know. I have hundreds of examples.How does a building inspector say this is a "correction", when there is no code violation?
Bluffing. Either from ignorance or arrogance.How does a building inspector say this is a "correction", when there is no code violation?
In my opinion, you "designate" it on the plans, analogous to how you show 60" turning circle on the plans to demonstrate to the plan checker that you have provided enough designated space for wheelchair maneuvering.Show How you "designate" the space.
Code does not say to whom, therefore, designate to all.
Show How you "designate" the space to others.
In San Diego that is reviewed during plan check and sometimes at final.I don't know of a IBC or ANSI 117.1 section that requires ISA on an accessible seating space at a table. The biggest problem I have with accessible tables is they use tables that have a center column all the time which does not allow for the toe space because of the large round base or X base. Just wondering if others fail accessibility inspections because of this because I do every time when an accessible seating space is required.
We would do the same. At plan check, if the tables show a center column (we all know they don't always show that), I make them detail the accessible one with at least a plan view showing how it will meet the minimum clear requirements.I don't know of a IBC or ANSI 117.1 section that requires ISA on an accessible seating space at a table. The biggest problem I have with accessible tables is they use tables that have a center column all the time which does not allow for the toe space because of the large round base or X base. Just wondering if others fail accessibility inspections because of this because I do every time when an accessible seating space is required.
Good one Mark, code clarification required?Show How you "designate" the space.