I have a project for a massive church facility here in California. The intent of the project is to create a classroom building for kindergarten and transitional kindergarten. No day care. We have chosen to use a code exception and we are getting a bit of push back. This is an existing building owned by the church and we will just be doing interior improvements.
2019 CBC section 305.1 Accessory to places of religious worship. Religious education rooms and religious auditoriums which are accessory to places of worship in accordance with section 303.1.4 and have occupant loads of less than 100 per room or space, shall be classified as Group A-3 occupancies.
The plan reviewer has provided this interpretation/correction:
Per Building Official: Upon review of your plans, per CBC 305.2.1 Within Places of Religious Worship - Worship Rooms and spaces within places
of religious worship providing such day care during religious functions shall be classified as part of the primary occupancy where not licensed
for day-care purposes by the Department of Social Services.
Interpretation: This building on a different parcel would not qualify as “within places of religious worship”
This project has nothing to do with day care during religious functions. So that is easily explained. But the "interpretation" that this building is on a "different parcel" so it would not qualify as being "within places of religious worship" is the problem, but does not seem like it should be. This church campus is situated on probably 10 city blocks worth of various buildings and facilities. This parcel/building is immediately adjacent to the campus and next door to a 400+ car church overflow parking lot.
I do not buy that because it is a different parcel that the code exception would not be valid. What do you think?
2019 CBC section 305.1 Accessory to places of religious worship. Religious education rooms and religious auditoriums which are accessory to places of worship in accordance with section 303.1.4 and have occupant loads of less than 100 per room or space, shall be classified as Group A-3 occupancies.
The plan reviewer has provided this interpretation/correction:
Per Building Official: Upon review of your plans, per CBC 305.2.1 Within Places of Religious Worship - Worship Rooms and spaces within places
of religious worship providing such day care during religious functions shall be classified as part of the primary occupancy where not licensed
for day-care purposes by the Department of Social Services.
Interpretation: This building on a different parcel would not qualify as “within places of religious worship”
This project has nothing to do with day care during religious functions. So that is easily explained. But the "interpretation" that this building is on a "different parcel" so it would not qualify as being "within places of religious worship" is the problem, but does not seem like it should be. This church campus is situated on probably 10 city blocks worth of various buildings and facilities. This parcel/building is immediately adjacent to the campus and next door to a 400+ car church overflow parking lot.
I do not buy that because it is a different parcel that the code exception would not be valid. What do you think?