Hi,
I have 3 questions regarding cleanouts required for a 115ft run of 4inch which will y connect into sewer main in front of house.
1.) The run has to make 2 90 degree turns, one about 20ft from the beginning of the run and one about 10 ft from the end of the downhill run where it y connects into sewer. My understanding of section 708.3.3, is that I can eliminate the requirement of a cleanout at the turn point if I instead use 2 45's and separate them with a straight piece, thus eliminating any turn greater than 45 degrees:
IPC - 708.3.3 Changes of direction.
Cleanouts shall be installed at each change of direction greater than 45 degrees (0.79 rad) in the building sewer, building drain and horizontal waste or soil lines. Where more than one change of direction occurs in a run of piping, only one cleanout shall be required for each 40 feet (12 192 mm) of developed length of the drainage piping.
2.) The horizontal Y where I tie into the main sewer line will be just downstream of a cleanout in front of my house. My interpretation of 708.3.5 is that I will not need a cleanout at the junction since a cleanout is already there within 10ft:
IPC - 708.3.5 Building drain and building sewer junction.
There shall be a cleanout near the junction of the building drain and the building sewer. The cleanout shall be either inside or outside the building wall and shall be brought up to the finished ground level or to the basement floor level. An approved two-way cleanout is allowed to be used at this location to serve as a required cleanout for both the building drain and building sewer. The cleanout at the junction of the building drain and building sewer shall not be required if the cleanout on a 3-inch (76 mm) or larger diameter soil stack is located within a developed length of 10 feet (3048 mm) of the building drain and building sewer connection. The minimum size of the cleanout at the junction of the building drain and building sewer shall comply with Section 708.7.
IPC - 708.3.4 Base of stack.
3.) Final question: Cleanouts should always be located above upstream from the junction points, correct?
Closing Note: My aim is to use one 4" cleanout for the entire one (in addition to a 2" cleanout at the fixture which joins to the the 4" line.)
Appreciate any knowledge on this subject in advance.
I have 3 questions regarding cleanouts required for a 115ft run of 4inch which will y connect into sewer main in front of house.
1.) The run has to make 2 90 degree turns, one about 20ft from the beginning of the run and one about 10 ft from the end of the downhill run where it y connects into sewer. My understanding of section 708.3.3, is that I can eliminate the requirement of a cleanout at the turn point if I instead use 2 45's and separate them with a straight piece, thus eliminating any turn greater than 45 degrees:
IPC - 708.3.3 Changes of direction.
Cleanouts shall be installed at each change of direction greater than 45 degrees (0.79 rad) in the building sewer, building drain and horizontal waste or soil lines. Where more than one change of direction occurs in a run of piping, only one cleanout shall be required for each 40 feet (12 192 mm) of developed length of the drainage piping.
2.) The horizontal Y where I tie into the main sewer line will be just downstream of a cleanout in front of my house. My interpretation of 708.3.5 is that I will not need a cleanout at the junction since a cleanout is already there within 10ft:
IPC - 708.3.5 Building drain and building sewer junction.
There shall be a cleanout near the junction of the building drain and the building sewer. The cleanout shall be either inside or outside the building wall and shall be brought up to the finished ground level or to the basement floor level. An approved two-way cleanout is allowed to be used at this location to serve as a required cleanout for both the building drain and building sewer. The cleanout at the junction of the building drain and building sewer shall not be required if the cleanout on a 3-inch (76 mm) or larger diameter soil stack is located within a developed length of 10 feet (3048 mm) of the building drain and building sewer connection. The minimum size of the cleanout at the junction of the building drain and building sewer shall comply with Section 708.7.
IPC - 708.3.4 Base of stack.
3.) Final question: Cleanouts should always be located above upstream from the junction points, correct?
Closing Note: My aim is to use one 4" cleanout for the entire one (in addition to a 2" cleanout at the fixture which joins to the the 4" line.)
Appreciate any knowledge on this subject in advance.