Working on plans for an escape room business (A-3). Occupant load of 123 people.
II-B construction existing building, non sprinklered.
1-hr rated corridor is required.
I am located in NC so I will be making reference to NC Building Code (NCBC).
NCBC 1020 states rated corridors shall comply with Section 708 Fire partitions.
Section 708.9: Ducts and air transfer openings shall comply with Section 717.
I know I need fire dampers, but my question is related to smoke dampers:
Section 717.5.3.1 Corridors
3. Listed smoke damper designed to resist passage of smoke shall be provided at each point a duct penetrates a corridor enclosure "required to have smoke and draft control doors in accordance with Section 716.5.3"
(exceptions of this section do not apply to me in this case)
Section 716.5.3 Door assemblies in corridors and smoke barriers
Section 716.5.3.1 Smoke and draft control
I am needing some guidance on the last two sections. Does this section mean that all rated corridors (regardless of whether it is considered a smoke barrier or not) are required to have smoke and draft control or does this section only apply if the assembly is a "corridor and a smoke barrier".
Thanks!
II-B construction existing building, non sprinklered.
1-hr rated corridor is required.
I am located in NC so I will be making reference to NC Building Code (NCBC).
NCBC 1020 states rated corridors shall comply with Section 708 Fire partitions.
Section 708.9: Ducts and air transfer openings shall comply with Section 717.
I know I need fire dampers, but my question is related to smoke dampers:
Section 717.5.3.1 Corridors
3. Listed smoke damper designed to resist passage of smoke shall be provided at each point a duct penetrates a corridor enclosure "required to have smoke and draft control doors in accordance with Section 716.5.3"
(exceptions of this section do not apply to me in this case)
Section 716.5.3 Door assemblies in corridors and smoke barriers
Section 716.5.3.1 Smoke and draft control
I am needing some guidance on the last two sections. Does this section mean that all rated corridors (regardless of whether it is considered a smoke barrier or not) are required to have smoke and draft control or does this section only apply if the assembly is a "corridor and a smoke barrier".
Thanks!