Yes, I have 8 classrooms tied to a large multi purpose/intervening space, where the classrooms all have secondary sliding door/wall section to open up to the intervening space.
They have designed to do that at the 75' common path limit is where you either can reach the exit outside or the corridor begins with double doors that connect to the main school corridor.
I asked for a furniture plan and they lost their mind. I asked for a hashed circulation path and they came back showing 44 inches.
I was expecting to see 72 inches with ties to the upper stair landing and 36 inch ties from each classroom door to the hashed circulation path.
I review at the SFMO and most big school district's have designers and inspectors that overlook these areas so or field inspectors fight it annually. Thx
IF they are only providing 44" clear, it's not an "E" corridor, it's an intervening room.
8 classrooms x 49 students = 392 occupants
392 x 0.15 = 58.8 inches for exit width in the intervening rooms.
If they want to treat it as a corridor, then 72" is the minimum width for "E" occupancies.
When treating the "collaboration" corridor as an intervening room, that room should also have its own occupant load in addition to the classroom load (because in my opinion the egress path width should be based on the assumption that all 8 classroom AND the collaboration space is occupied at the same time).
In my opinion, they also need to show required accessibility clearances around the door openings.
In our California Building Code, all this falls under CBC 107.2.1 "Information on construction documents."
From the architect's perspective, they probably aren't being paid to design every conceivable furniture layout, so that's probably what's causing them heartburn. I get that. But just like with any other multipurpose room, they have to be able to state all the proposed functions per Table 1004.5, and design the MOE path based on the worst-case / highest-occupancy. Then you inform the owner that any furniture layouts not shown on the plans will be subject to final inspection and approval by the local fire official. Even if they are keeping the classroom MOE paths clear, 1018.1 describes how furnishings placement creates aisles in the other collaboration spaces, and those are subject to final approval.
Multipurpose furniture plans can be reviewed now during plan check, or the school can take their chances by purchasing and installing furnishings "at risk" and then finding out afterward whether the fire official thinks it meets code or not.