ggm.arch
Hello all, maybe you guys can shed some light on a situation that I am in.
I'm dealing with a 838 sf B occupancy that my client is trying to rent as a
Thrift Shop so the BO requires a Change Of Occupancy and a New Occupancy Permit.
the space consists of three rooms, an office, a restroom(non ADA compliant) and the main room with a 36" front
door accessible route out said door to an accessible ramp to an accessible van parking space.
All separation requirements are existing. all the client needs to do is move in, no work on their end.
plumbing fixture count complies with IPC. There is no drinking fountain and it is exempt because
the occupancy would be less than 15. currently it is 9 occupants and the new occupancy is 13. Nothing
if forcing any kind of alteration expense, they said they didn't even need a drawing. Even if I were
to provide a drawing, it would show three rooms that state, "No work."
the code reviewer rejected my application for change of occupancy stating that .......
"The Design Professional shall consult with the Owner to upgrade the Toilet Facilities per 2021 IEBC
Section 306.1 and 306.7.11; and / or seek a Variance from the State Dept of Labor and Industries
Accessibility Advisory Board if not installing making the Alterations – or to install a 'Unisex' Toilet
Room; or for seeking a Variance from the Accessibility Advisory Board if determining the changes
to the Toilet Facilities are Technically Infeasible.
Provide a copy of the Variance ‘Fact of Findings’ to the Municipality."
I understand the comment, but my original argument based off the intent of the existing build code
is to bring existing buildings up to code over time and this is achieved by a proportional amount of alteration
based upon the amount spent on said alteration. (20% rule 306.7.1.1) Has this changed? is the "toilet facility,"
as indicated 306.7.1 actually saying "Accessible toilet facility?"
I was not reading anywhere in the IEBC that under any circumstance, the restroom Shall be Accessible
at any level of alteration no matter what is spent or even if nothing is spent. Am I wrong?
Is section 306.7.11 toilet rooms to be read that it is always required to have an accessible toilet facility
on the site. Or is it a function of the 20% rule where the amount of construction cost is high enough, though
impossible to adapt the existing toilet to comply that a new accessible restroom would be required?
how do you guys see alteration where no alteration is being done other than the CoO? If i'm wrong
I am completely willing to admit reading the code incorrectly, but I just am having trouble with this
reading.
any help is appreciated.
g
reading.
g