Given:
2018 IECC and project is located in climate zone 5A.
Minor remodel to an existing three story apartment building. It is non-substantial because the cost of the remodel ($20,000) is less than 50% of the overall value of the apartment building. And the energy use of the building is not being increased.
Plans were thoroughly review and approved during the permit application process.
The building inspector sees that the building owner is removing the old R13 batt insulation and replacing it with new R13 batt insulation.
Question:
Section C503 states that existing ceiling cavity need not comply with the requirements of new construction provided that these cavities are filled with insulation. Is it acceptable for the new insulation to be equal to the existing insulation but less than the prescribed value of R38?
As always, thanks in advance.
ICC Certified Plan Reviewer
NFPA Certified Fire Plan Examiner
2018 IECC and project is located in climate zone 5A.
Minor remodel to an existing three story apartment building. It is non-substantial because the cost of the remodel ($20,000) is less than 50% of the overall value of the apartment building. And the energy use of the building is not being increased.
Plans were thoroughly review and approved during the permit application process.
The building inspector sees that the building owner is removing the old R13 batt insulation and replacing it with new R13 batt insulation.
Question:
Section C503 states that existing ceiling cavity need not comply with the requirements of new construction provided that these cavities are filled with insulation. Is it acceptable for the new insulation to be equal to the existing insulation but less than the prescribed value of R38?
As always, thanks in advance.
ICC Certified Plan Reviewer
NFPA Certified Fire Plan Examiner