Horizontal Sheathing Wind Wall Bracing

TheCommish

SAWHORSE
Joined
Sep 27, 2011
Messages
2,181
Location
Charlton Ma
We're having an internal office discussion about continuous sheathing when wall bracing and whether low structural wood panel has to be vertical or can be horizontal with staggered end joints 2015 IRC 602.10 talks about full height sections.

I recall learning that either was appropriate but this may have changed over the code cycles.

If we've ridden this horse before point me to the discussion thank you.
 
Yes. Simply block the joints when using CS-WSP so that the edges can be nailed 6" o.c. Note that this only needs to be done where there is a BWP.
 

Attachments

  • blocking.jpg
    blocking.jpg
    52.8 KB · Views: 4
It depends on the use.For uplift vertical is better if the sheathing is 97" so it can span from top of the top plate to an overlap at the bottom plate.
For a blocked shear wall 2x4 blocking attached to the studs to transfer the loads.
 